For all you folks with electrician background out there, I have a question regarding the derating code. I recently had a NEMA14-50 outlet installed for charging my standard range model 3. I requested 6 gauge copper wire, outlet was only a couple of feet from the panel and everything seemed to have gone smoothly. I didn't realize until later that the electrician only installed a 40A breaker instead of 50A. When I asked him, he stated the 6/3 NM-B wire he used, which has a rating of 55A at 60C, must be 125% over the breaker size (hence 40A), which then must be 125% of the charging load of the car (32A). If a 50A breaker is to be installed, a #6 HTTN wire would be needed.
According to NEC 210.19:
"The minimum branch circuit conductor size shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load."
And the overcurrent protection code 625.40 also calls for a breaker that is no less than 125% of the maximum load of the EV car.
Both of these codes provide guidelines of the comparative amperage between the circuit/breaker and the charging load of the car. I don't see it mentioned, and I haven't come across it in my research, that the circuit amperage must be higher than the breaker. Am I missing something?
A 40A breaker satisfies my needs as my model 3 is charging at its max. But I read on various forums that a 50A breaker is usually what's installed with the #6 wiring and I want to make sure the job was done correctly and keep my options open for future upgrade. Thanks!