Hey Club,
Patiently awaiting my Model 3 and have been looking into home charging stuff.
I want to install a NEMA 14-50 outlet in the garage now and just use the included UMC when I get the 3. The UMC will stay plugged in to this outlet most of the time (save for maybe 3 or 4 roadtrips a year) so I'm not concerned with wear on the outlet. However, if down the road I want to upgrade to a HPWC I want to have the proper wiring so I can just remove the 14-50 and hardwire the HPWC without much hassle.
I've got plenty of room in a 200a panel to install a 50a breaker and run 6 gauge wire. I'll have a 70ish foot run from my breaker (in basement on one side of the house) through the floor joists in the unfinished basement and up to the garage on the other side of the house.
From what I'm seeing, the 14-50 outlet takes 4 wires (2 hots, a neutral, and a ground) but the HPWC only uses 3 (2 hots and a ground). Am I correct in assuming that I can just wire up the 14-50 properly with the 4 wires and then just not use the neutral later for the HPWC?
I'm handy and good at following instructions but I am an electrical rookie. Fortunately I have an electrical engineer friend that is going to help with the install, but he's not a Tesla guy hence why I ask the question here. After searching extensively on both google and these forums, I wasn't able to find an answer to this specific question. Can anyone assist? Thanks in advance.
Ninja edit for another question: The wall where the plug will be mounted is between the garage (no heat or A/C) and the house so the wall is insulated (just regular R-30 or whatever, not foam). Is there any issue running my 6 gauge wire inside this wall as far as a potentially warm wire contacting the insulation?
Patiently awaiting my Model 3 and have been looking into home charging stuff.
I want to install a NEMA 14-50 outlet in the garage now and just use the included UMC when I get the 3. The UMC will stay plugged in to this outlet most of the time (save for maybe 3 or 4 roadtrips a year) so I'm not concerned with wear on the outlet. However, if down the road I want to upgrade to a HPWC I want to have the proper wiring so I can just remove the 14-50 and hardwire the HPWC without much hassle.
I've got plenty of room in a 200a panel to install a 50a breaker and run 6 gauge wire. I'll have a 70ish foot run from my breaker (in basement on one side of the house) through the floor joists in the unfinished basement and up to the garage on the other side of the house.
From what I'm seeing, the 14-50 outlet takes 4 wires (2 hots, a neutral, and a ground) but the HPWC only uses 3 (2 hots and a ground). Am I correct in assuming that I can just wire up the 14-50 properly with the 4 wires and then just not use the neutral later for the HPWC?
I'm handy and good at following instructions but I am an electrical rookie. Fortunately I have an electrical engineer friend that is going to help with the install, but he's not a Tesla guy hence why I ask the question here. After searching extensively on both google and these forums, I wasn't able to find an answer to this specific question. Can anyone assist? Thanks in advance.
Ninja edit for another question: The wall where the plug will be mounted is between the garage (no heat or A/C) and the house so the wall is insulated (just regular R-30 or whatever, not foam). Is there any issue running my 6 gauge wire inside this wall as far as a potentially warm wire contacting the insulation?