Several thoughts:
1. You should not need the disconnect switch on a receptacle for sure, or even on a Wall Connector. (Unless you are in Canada or somewhere with different rules?) at least not st 60a or below.
2. Does the receptacle option include a GFCI breaker? That cost seems artificially low. GFCI is required by US NEC ok the receptacle, but NOT on the wall connector, so it saves most folks a about $100.
3. If you go the wall connector route it lets you keep the UMC in your car at all times which is a nice feel good safety measure.
4. If you go the wall connector route I would probably want to do a 60a circuit so you could enable a full 48a charge rate if your vehicle supports it. This can be accomplished with 6 gauge wire if it can be used at the 75c rating. So romex does not meet this (due to a code requirement for it to be treated at 60c). SE wire does, MC does, or THHN in any kind of conduit.
I am a massive wall connector fan. You won’t be disappointed.
Thanks! I'm just in PA outside of Philadelphia...so no different rules...
Interestingly, this guy was the only one of the 5 electricians I consulted who said I needed the disconnect, but he was also the cheapest. I guess I figured that the disconnect served the same purpose of the GFCI (which none of the other electricians mentioned at all)...
So I just let it go and figured he knows what he's doing...
I worry about "challenging" the guy at this point, since it's his profession... any advice on how to proceed?
I like the idea of the wall connector but I'm already pretty disappointed that the charger install is as much as it is, so trying to limit spend as much as possible.