NEMA 15-50R to 14-50R

Discussion in 'Model S: Battery & Charging' started by Kickin, Jun 20, 2015.

  1. Kickin

    Kickin Member

    Joined:
    Feb 4, 2015
    Messages:
    53
    Location:
    Camillus, NY
    I'm visiting my son in Georgia in a few weeks, and will be taking my new Tesla. His ice cream shop has two ice cream makers that use a 3-phase 15-50R. I'm looking for an adapter to (or make my own) allow the S to charge from those outlets. Am I right in that all I need to do is use 2 out of the 3 legs to get 208V? Is this safe and has anyone been successful in charging the model S on this type of plug?

    Thanks!

    This is what his plugs look like:

    337088-ProductImageURL.jpg
     
  2. Saghost

    Saghost Active Member

    Joined:
    Oct 9, 2013
    Messages:
    3,035
    Location:
    Delaware
    I've never seen an outlet like that before, but your approach sounds correct. US Model Ss are equipped to handle single phase only (European cars have three phase chargers...)

    I believe a lot of EVSEs at commercial sites are wired as you describe, at 208V.
    Walter
     
  3. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    They are a little pricey, but your idea should work.

    HUBBELL HBL8452C AC Plug NEMA 15-50 Male Angled - Electric Plugs - Amazon.com $64.00 + $9.99 shipping

    Wiring Diagram 15-50P.PNG

    Just remember that this will be the same as a 6-50 to 14-50 adapter. There is no neutral to connect to the neutral in the 14-50. The UMC will work, but label the adapter very well so that an RV user will not use it and blow many of their 120V devices.
     
  4. Kickin

    Kickin Member

    Joined:
    Feb 4, 2015
    Messages:
    53
    Location:
    Camillus, NY
    Awesome Cottonwood, thanks!!!

    Also found this in an EVSE wiring manual...

    Make an adapter using this....PNG
     
  5. Cosmacelf

    Cosmacelf Active Member

    Joined:
    Mar 6, 2013
    Messages:
    3,399
    Location:
    San Diego
    Sounds workable, but someone who understands commercial 3 phase power, like FlasherZ, should weigh in. Looks like you would connect the grounds together and then X and Z from the 15-50 to the two hots of the 14-50, and leave the 14-50 neutral unconnected. Use 6 gauge wire for the interconnect.
     
  6. Kickin

    Kickin Member

    Joined:
    Feb 4, 2015
    Messages:
    53
    Location:
    Camillus, NY
    Yes, I was thinking of using X/Y and leaving out Z, but I guess it doesn't matter? No need to connect W of the 14-50 to anything?

    1.PNG 2.PNG
     
  7. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    Yes, G to G, X to X, and Y to Y should work fine for the Tesla UMC, leaving Z (Phase 3) unconnected on the 15-50 and W (neutral) unconnected on the 14-50. W (neutral) unconnected on the 14-50 can produce unexpected voltage for an RV or other use that is expecting 120 Volts, W to X, and W to Y. That is why the adapter needs to be clearly and boldly labeled "Only for Tesla Charging, Not for RV Use" or something like that.

    See NEMA connector - Blade identification - Wikipedia for reference.
     
  8. Kickin

    Kickin Member

    Joined:
    Feb 4, 2015
    Messages:
    53
    Location:
    Camillus, NY
    That's just what I needed, Thanks! I'll test voltages on the 14-50 before I actually connect the UMC to make sure everything looks good!
     
  9. deonb

    deonb Active Member

    Joined:
    Mar 4, 2013
    Messages:
    3,020
    Location:
    Redmond, WA
    Isn't that just an open circuit? Similar to a circuit with a switch on the neutral.

    You typically don't want to switch neutral due to human safety reasons, but it doesn't harm 110V equipment if you do. (It doesn't work of course... but it's not harmful).
     
  10. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    It's not an open circuit. It's very harmful to 120V equipment. Remember that neutral is a grounded center-tap of the transformer that carries the imbalance between leg 1 & leg 2. Allow it to float, and you'll get imbalanced voltages based on the current drawn across the legs.

    Imagine appliance 1 between L1 and neutral, and appliance 2 between neutral and L2. Current will flow; the completed circuit is L1-app1-N-app2-L2, with neutral floating.

    - - - Updated - - -

    For most 3-phase power, this will work. You may end up with 208V or 240V, depending on whether it's a wye or delta configuration. The 18-series receptacle is for wye when neutral is required, the 15-series receptacle can be used for delta or wye when only L-L is needed. The wiring Cosmacelf spoke of will work either way. As mentioned, label that adapter 6 ways from Sunday with "NO NEUTRAL - TESLA CHARGING ONLY".
     
  11. deonb

    deonb Active Member

    Joined:
    Mar 4, 2013
    Messages:
    3,020
    Location:
    Redmond, WA
    Right, of course - you still have the neutral connected between the 2 legs on the other side of the circuit. My bad.
     
  12. Kickin

    Kickin Member

    Joined:
    Feb 4, 2015
    Messages:
    53
    Location:
    Camillus, NY
    Thanks FlasherZ! I'll be sure to label it properly :)
     