NEMA 15-50R to 14-50R

Kickin

Member
Feb 4, 2015
66
38
Camillus, NY
I'm visiting my son in Georgia in a few weeks, and will be taking my new Tesla. His ice cream shop has two ice cream makers that use a 3-phase 15-50R. I'm looking for an adapter to (or make my own) allow the S to charge from those outlets. Am I right in that all I need to do is use 2 out of the 3 legs to get 208V? Is this safe and has anyone been successful in charging the model S on this type of plug?

Thanks!

This is what his plugs look like:

337088-ProductImageURL.jpg
 

Saghost

Well-Known Member
Oct 9, 2013
8,224
7,087
Delaware
I've never seen an outlet like that before, but your approach sounds correct. US Model Ss are equipped to handle single phase only (European cars have three phase chargers...)

I believe a lot of EVSEs at commercial sites are wired as you describe, at 208V.
Walter
 

Cottonwood

Roadster#433, Model S#S37
Feb 27, 2009
5,088
174
Colorado
They are a little pricey, but your idea should work.

HUBBELL HBL8452C AC Plug NEMA 15-50 Male Angled - Electric Plugs - Amazon.com $64.00 + $9.99 shipping

Wiring Diagram 15-50P.PNG


Just remember that this will be the same as a 6-50 to 14-50 adapter. There is no neutral to connect to the neutral in the 14-50. The UMC will work, but label the adapter very well so that an RV user will not use it and blow many of their 120V devices.
 

Cosmacelf

Well-Known Member
Mar 6, 2013
9,029
23,731
San Diego
Sounds workable, but someone who understands commercial 3 phase power, like FlasherZ, should weigh in. Looks like you would connect the grounds together and then X and Z from the 15-50 to the two hots of the 14-50, and leave the 14-50 neutral unconnected. Use 6 gauge wire for the interconnect.
 

Cottonwood

Roadster#433, Model S#S37
Feb 27, 2009
5,088
174
Colorado
Yes, I was thinking of using X/Y and leaving out Z, but I guess it doesn't matter? No need to connect W of the 14-50 to anything?

View attachment 84852View attachment 84853

Yes, G to G, X to X, and Y to Y should work fine for the Tesla UMC, leaving Z (Phase 3) unconnected on the 15-50 and W (neutral) unconnected on the 14-50. W (neutral) unconnected on the 14-50 can produce unexpected voltage for an RV or other use that is expecting 120 Volts, W to X, and W to Y. That is why the adapter needs to be clearly and boldly labeled "Only for Tesla Charging, Not for RV Use" or something like that.

See NEMA connector - Blade identification - Wikipedia for reference.
 

Kickin

Member
Feb 4, 2015
66
38
Camillus, NY
Yes, G to G, X to X, and Y to Y should work fine for the Tesla UMC, leaving Z (Phase 3) unconnected on the 15-50 and W (neutral) unconnected on the 14-50. W (neutral) unconnected on the 14-50 can produce unexpected voltage for an RV or other use that is expecting 120 Volts, W to X, and W to Y. That is why the adapter needs to be clearly and boldly labeled "Only for Tesla Charging, Not for RV Use" or something like that.

See NEMA connector - Blade identification - Wikipedia for reference.

That's just what I needed, Thanks! I'll test voltages on the 14-50 before I actually connect the UMC to make sure everything looks good!
 

deonb

Active Member
Mar 4, 2013
4,061
4,361
Redmond, WA
W (neutral) unconnected on the 14-50 can produce unexpected voltage for an RV or other use that is expecting 120 Volts, W to X, and W to Y. That is why the adapter needs to be clearly and boldly labeled "Only for Tesla Charging, Not for RV Use" or something like that.

Isn't that just an open circuit? Similar to a circuit with a switch on the neutral.

You typically don't want to switch neutral due to human safety reasons, but it doesn't harm 110V equipment if you do. (It doesn't work of course... but it's not harmful).
 

FlasherZ

Sig Model S + Sig Model X + Model 3 Resv
Jun 21, 2012
7,028
1,025
Isn't that just an open circuit? Similar to a circuit with a switch on the neutral.

You typically don't want to switch neutral due to human safety reasons, but it doesn't harm 110V equipment if you do. (It doesn't work of course... but it's not harmful).

It's not an open circuit. It's very harmful to 120V equipment. Remember that neutral is a grounded center-tap of the transformer that carries the imbalance between leg 1 & leg 2. Allow it to float, and you'll get imbalanced voltages based on the current drawn across the legs.

Imagine appliance 1 between L1 and neutral, and appliance 2 between neutral and L2. Current will flow; the completed circuit is L1-app1-N-app2-L2, with neutral floating.

- - - Updated - - -

Sounds workable, but someone who understands commercial 3 phase power, like FlasherZ, should weigh in. Looks like you would connect the grounds together and then X and Z from the 15-50 to the two hots of the 14-50, and leave the 14-50 neutral unconnected. Use 6 gauge wire for the interconnect.

For most 3-phase power, this will work. You may end up with 208V or 240V, depending on whether it's a wye or delta configuration. The 18-series receptacle is for wye when neutral is required, the 15-series receptacle can be used for delta or wye when only L-L is needed. The wiring Cosmacelf spoke of will work either way. As mentioned, label that adapter 6 ways from Sunday with "NO NEUTRAL - TESLA CHARGING ONLY".
 

deonb

Active Member
Mar 4, 2013
4,061
4,361
Redmond, WA
It's not an open circuit. It's very harmful to 120V equipment. Remember that neutral is a grounded center-tap of the transformer that carries the imbalance between leg 1 & leg 2. Allow it to float, and you'll get imbalanced voltages based on the current drawn across the legs.

Imagine appliance 1 between L1 and neutral, and appliance 2 between neutral and L2. Current will flow; the completed circuit is L1-app1-N-app2-L2, with neutral floating.

Right, of course - you still have the neutral connected between the 2 legs on the other side of the circuit. My bad.
 
It's not an open circuit. It's very harmful to 120V equipment. Remember that neutral is a grounded center-tap of the transformer that carries the imbalance between leg 1 & leg 2. Allow it to float, and you'll get imbalanced voltages based on the current drawn across the legs.

Imagine appliance 1 between L1 and neutral, and appliance 2 between neutral and L2. Current will flow; the completed circuit is L1-app1-N-app2-L2, with neutral floating.

- - - Updated - - -



For most 3-phase power, this will work. You may end up with 208V or 240V, depending on whether it's a wye or delta configuration. The 18-series receptacle is for wye when neutral is required, the 15-series receptacle can be used for delta or wye when only L-L is needed. The wiring Cosmacelf spoke of will work either way. As mentioned, label that adapter 6 ways from Sunday with "NO NEUTRAL - TESLA CHARGING ONLY".

Thanks FlasherZ! I'll be sure to label it properly :)
 

Products we're discussing on TMC...

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.