NEMA 6-50 vs 14-50

This site may earn commission on affiliate links.
The clipper creek is three wires with Hot/Hot/Ground, no neutral. There's 240V between the two hots, and 120V from each of those to ground, but under normal operation there's no current on the ground wire. A 10-X device is Hot/Hot/Neutral-Ground, a 6-X device is Hot/Hot/Ground. Electrically the third wire is mostly the same, but the former the device is allowed to draw unbalanced current from the hot legs and return the imbalance through the third wire, the latter must draw and return through the hot legs only, the ground is only for safety.

You can swap out the 10-50 for a 6-50 by changing third wire to ground, but there are code implications in the marking of the wire and which bus it is on if there's a subpanel in the mix.

I see. That makes sense. I guess I need to see what the wiring truly is. Unclear how he is grounding the device...what a mess...
 
The clipper creek is three wires with Hot/Hot/Ground, no neutral. There's 240V between the two hots, and 120V from each of those to ground, but under normal operation there's no current on the ground wire. A 10-X device is Hot/Hot/Neutral-Ground, a 6-X device is Hot/Hot/Ground. Electrically the third wire is mostly the same, but the former the device is allowed to draw unbalanced current from the hot legs and return the imbalance through the third wire, the latter must draw and return through the hot legs only, the ground is only for safety.

You can swap out the 10-50 for a 6-50 by changing third wire to ground, but there are code implications in the marking of the wire and which bus it is on if there's a subpanel in the mix.

Please do not give people this incorrect information!

A 10-series device is a line(hot)/line(hot)/neutral device, not "neutral-ground" and electrically they're not "mostly the same" especially when subpanels and/or detached structures are involved. The grounded circuit conductor (a/k/a "neutral") and equipment grounding conductor (a/k/a "ground") are two distinct items. The *only* place they are one and the same is the bus bar in one single service panel from any power company connection. Everywhere else they are separate (minimal exceptions apply for older outbuildings and such, I won't cover them here).

While it will work to do as you say, it is not safe in many circumstances to simply "change the third wire to ground"... There are key safety reasons the code has eliminated all combined grounded/grounding systems, for branch circuits in 1996 and for detached structures in 2005/2008. For example, if a neutral conductor fails between the service panel and a detached garage subpanel, and the charging unit's ground in that detached garage is connected to neutral, then unbalanced return current for that subpanel can return to the service panel and transformer through a person touching the metal case of the device and standing on the floor. It happens more than you might think.

The only safe and legal way to do this is to open both the receptacle and the panel to which the receptacle terminates, ensure the former neutral wire is moved to a bus with all the grounds (in the service panel this will be one and the same, otherwise it will be a separate electric bus), remark the wire with green tape on both ends, then install the 6-50 outlet. Note that remarking a white wire as green is only legal per code when it is part of a multi-wire cable assembly, but it's something many inspectors will pass anyway, as long as it is clearly marked green.

- - - Updated - - -

Again, I'm clearly the least educated of your guys w/r to this stuff, but these diagrams seem to suggest the only difference between 10-50 and 14-50 is the ground protection.

Correct. The 10 series receptacles were WW2-era connections, grounding appliances using the neutral on 125V/250V appliances. The belief was that is was relatively safe because at the time, neutral and ground were mixed interchangeably. However, certain failure scenarios created significant harm for humans - shocks and death. I can recall getting one hell of a shock when I was a child at my great-grandmother's house because I ended up forming the return path for current on a broken neutral for her oven clock via the kitchen sink. That would not have happened post-1996 NEC.
 
So I spoke to the electrician, here's his response (does this make sense?):

____________________________________________________________

Quick foliow-up question, did you install a four wire cable (hot-hot-neutral-ground) or three wire (hot-hot-neutral) to ####’s garage? It will help me figure out the best way to be able to charge my Tesla. I need to make sure I get the right type of adapter.

_____________________________________________________________

I installed a three wire but I can change it to a 4 wire pretty easily
Thanks, [electrician]

_______________________________________________________

Is that code? I thought you had to have a ground, especially with high voltages.

____________________________________________________________

The charger called for 2 hots and one ground. Yes every circuit needs a ground not all need a neutral.....AC, HEATER, H20 HEATER WELDERS ETC. What you are looking for is a neutral....you have 2 hots 1 ground....3 wire.......4 wire has a neutral
 
So I spoke to the electrician, here's his response (does this make sense?):

____________________________________________________________

Quick foliow-up question, did you install a four wire cable (hot-hot-neutral-ground) or three wire (hot-hot-neutral) to ####’s garage? It will help me figure out the best way to be able to charge my Tesla. I need to make sure I get the right type of adapter.

_____________________________________________________________

I installed a three wire but I can change it to a 4 wire pretty easily
Thanks, [electrician]

_______________________________________________________

Is that code? I thought you had to have a ground, especially with high voltages.

____________________________________________________________

The charger called for 2 hots and one ground. Yes every circuit needs a ground not all need a neutral.....AC, HEATER, H20 HEATER WELDERS ETC. What you are looking for is a neutral....you have 2 hots 1 ground....3 wire.......4 wire has a neutral

He probably did not understand that a 10-50 is wired as Hot-Hot-Neutral. Just ask him to change it to a 6-50. Tesla make a 6-50 and a 10-30 adapter for the UMC, but not a 10-50 adapter.
 
The charger called for 2 hots and one ground. Yes every circuit needs a ground not all need a neutral.....AC, HEATER, H20 HEATER WELDERS ETC. What you are looking for is a neutral....you have 2 hots 1 ground....3 wire.......4 wire has a neutral

He says this, but he installed an ungrounded 125V/250V outlet on it which requires a neutral? Yikes.

You're probably ok, is there only one circuit panel at your in-laws' home? If so, you should just remark the white conductor with green tape (on both sides) and swap it for a 6-50. Not the right-the-first-time solution but it won't be compromised from a safety perspective.

If she has more than one circuit panel, then you'll have to inspect where the ground is connected to determine what needs to be done.
 
He probably did not understand that a 10-50 is wired as Hot-Hot-Neutral. Just ask him to change it to a 6-50. Tesla make a 6-50 and a 10-30 adapter for the UMC, but not a 10-50 adapter.

He says this, but he installed an ungrounded 125V/250V outlet on it which requires a neutral? Yikes.

You're probably ok, is there only one circuit panel at your in-laws' home? If so, you should just remark the white conductor with green tape (on both sides) and swap it for a 6-50. Not the right-the-first-time solution but it won't be compromised from a safety perspective.

If she has more than one circuit panel, then you'll have to inspect where the ground is connected to determine what needs to be done.

Thanks for the response. Exactly what I was thinking.
 
Always use ground wire, neutral is not required for 240V Split Phase.

Voltage over 25V is required to have ground wire, Sometimes 20V AC (split phase, neutral is not required) Make sure that you have ground wire connected, consult your local code or NEC.



My mother-in-law installed a Clipper Creek charger for her Volt. The electrician installed a plug for me so I could charge my Tesla via the mobile charger rather than via the J1772. Unfortunately,
- the guy installed a 10-50 plug which has no adapter (kind of a dead standard)
- He ran a 3 cable wire without a ground (hot-hot-neutral)

Anyway, I am going to replace the plug and re-wire it. My question is can I just swap out the plug and wire the ground to the receptacle? The Clipper Creek device will also need to be grounded to that...

Any opinions/thoughts from the electrical engineers in the crowd (no idea why these pics are sideways)?

View attachment 43850View attachment 43853
View attachment 43851View attachment 43852

http://www.qualtekusa.com/PDFs/nema_nonlocking_configuration_chart.pdf