One of the things that I looked for prior to ordering my Model 3 was whether anyone else had experience of having a new electrical supply installed in a remote garage. I didn't find many real-world examples so have gone through the process of requesting a quote from my local DNO, Northern Power Grid.
I was hoping that the supply would be on my side of the street and therefore avoid digging up the road to keep costs down but that's not the case.
Their quote for a new connection crossing 6m of road and 8m of driveway to a meter inside my garage is £3300 including VAT
Assuming 5p/kwh evening rate on an ev tarrif and 50p/kwh from a public charger gives a 45p/kwh difference. This equates to a break-even value of 7300KWh or ~30,000 miles at 4m/kwh or 2 years.
On the other end of the scale, 15p/KWh home and 30p/KWh public costs would increase this to 88,000 miles.
Does anyone have experience of groundworks costs, specifically whether the £1200 for digging my drive could be reduced significantly?
Description of the Works Unit/Measure Charge (£)
Install a single phase service, from a passing main including a
mains service joint, excavate and backfill joint hole £807.00
Additional excavation in typical tarmac footpath 8m £756.00
Additional excavation in typical road 6m £1,007.00
Additional cable 16m £178.00
Price of the Works £2,748.00
VAT At 20% £549.60
Total Cost £3,297.60
Technical Summary:
Connection voltage 230V
Number of phases Single
Frequency 50Hz
Maximum capacity 18kW
VAT At 20% £549.60
Technical Summary:
Frequency 50Hz