New install yesterday but they gave me a smaller inverter than quoted.

SunnyInVegas

Member
Dec 2, 2020
29
9
Las Vegas, NV
My 12.24kw system got installed yesterday and everything went well. I’m in Las Vegas.

I ordered in late August and got installed Dec. 1.

My spec sheets indicated I would receive the SE11400, but they installed the 10000 unit instead. They installer said it didn’t matter and don’t worry.

Should I insist they change it to the SE11400 unit, or does it really not make a difference?
 

wwhitney

Member
Nov 2, 2017
748
905
Berkeley, CA
More information about your install would be needed to know if it would make a difference. It may make 0 difference (in which case one wonders why the designers specified the larger inverter) or it may make a small difference. It's very unlikely the economic value of the difference exceeds the labor cost of swapping out to a larger inverter. So if you determine that it does make a difference, the optimal solution would be ask for a small rebate on the cost of the system because of the equipment substitution.

Cheers, Wayne
 

Vines

Active Member
Jul 20, 2018
1,783
2,062
Silicon Valley, CA
Only issue to note is your DC/AC ratio is now near 1.23, instead of 1.07 or so. There will be some clipping of maximum power, whether that leads to a lower total energy harvest is a more complicated question. I know SE systems are tolerant of relatively high stacking ratios, and others have pointed out @nwdiver that there is a very small total energy harvest loss even with clipping up to higher stacking ratios.
 
  • Helpful
Reactions: jjrandorin

SunnyInVegas

Member
Dec 2, 2020
29
9
Las Vegas, NV
Thanks for the quick reply.

My system is a 36 panel 12.24kW system with 1 inverter. 200A main breaker panel. I have 31 panels on the south facing roof maxing out my available space there. The remaining 5 panels are on the north facing roof but they still have very good sun exposure. I have 2x powerwalls. Is there more info I can provide to help?
 

getakey

Member
Jan 28, 2020
985
307
95762
Thanks for the quick reply.

My system is a 36 panel 12.24kW system with 1 inverter. 200A main breaker panel. I have 31 panels on the south facing roof maxing out my available space there. The remaining 5 panels are on the north facing roof but they still have very good sun exposure. I have 2x powerwalls. Is there more info I can provide to help?

you beat my post
 

adspguy

Member
Dec 1, 2016
139
107
Bedford MA
my 36 panel 12.24kw system has a 10000 solaredge inverter which is what was specified as well. 3 powerwalls in my system. It was recently installed so I haven't got to see what the full summer performance is.
 
  • Informative
Reactions: jjrandorin

wwhitney

Member
Nov 2, 2017
748
905
Berkeley, CA
My system is a 36 panel 12.24kW system with 1 inverter. 200A main breaker panel. I have 31 panels on the south facing roof maxing out my available space there. The remaining 5 panels are on the north facing roof but they still have very good sun exposure.
What is your roof slope on the north and south?

If your roof slope is 12:12, then when the sun is perpendicular to your south panels (maximum irradiance), there's no sun on your north panels. So your maximum DC power is effectively 31/36 * 12.24 = 10.54 kW DC. Very reasonable to have on a 10 kW AC inverter, you'll have little or no clipping.

While if your roof "slope" were 0:12, then there'd be no difference, and you have the possible worst case clipping of the DC/AC ratio of 1.23. Even that wouldn't be too bad, and of course that would only be if your house was in the tropics so the sun was sometimes directly overhead.

In between, you get a blend of the two extreme cases. If you provide the roof slope, and the azimuth (how far off true south your "south" roof faces), then if I get a chance I'll do a little vector math to see if your panels could every actually produce enough power at STC to cause your inverter to clip.

Cheers, Wayne
 
  • Helpful
Reactions: jjrandorin

h2ofun

Active Member
Aug 11, 2020
1,232
192
auburn, ca
My 12.24kw system got installed yesterday and everything went well. I’m in Las Vegas.

I ordered in late August and got installed Dec. 1.

My spec sheets indicated I would receive the SE11400, but they installed the 10000 unit instead. They installer said it didn’t matter and don’t worry.

Should I insist they change it to the SE11400 unit, or does it really not make a difference?

Two reasons I have always had the largest inverter put in. First, with my 47 panels and a 11400, I do see some clipping during the summer. at 133% spec, 47 is the most panels I can have, 14.5K, on a 11400.

Second, is what if you want to put more panels on? So if the contract said 11400, I would insist on the 11400, even if you do not need it now. They can easily say you do not.

If I split my system, technologically, I could get away with a 3800 and 7600. But I have insisted I want 2 11400's, one I have now, and a new one, which I have also asked I want the EV port, even though I would have zero plans to use.
 
  • Informative
Reactions: jjrandorin

jedmo

Member
Sep 9, 2020
107
35
Northern California
What is your roof slope on the north and south?

If your roof slope is 12:12, then when the sun is perpendicular to your south panels (maximum irradiance), there's no sun on your north panels. So your maximum DC power is effectively 31/36 * 12.24 = 10.54 kW DC. Very reasonable to have on a 10 kW AC inverter, you'll have little or no clipping.

While if your roof "slope" were 0:12, then there'd be no difference, and you have the possible worst case clipping of the DC/AC ratio of 1.23. Even that wouldn't be too bad, and of course that would only be if your house was in the tropics so the sun was sometimes directly overhead.

In between, you get a blend of the two extreme cases. If you provide the roof slope, and the azimuth (how far off true south your "south" roof faces), then if I get a chance I'll do a little vector math to see if your panels could every actually produce enough power at STC to cause your inverter to clip.

Cheers, Wayne

Just wanted to note, there are a lot of smart and helpful people on these forums...me not being one of the smart ones. cheers!
 
  • Like
Reactions: jjrandorin

SunnyInVegas

Member
Dec 2, 2020
29
9
Las Vegas, NV
What is your roof slope on the north and south?

If your roof slope is 12:12, then when the sun is perpendicular to your south panels (maximum irradiance), there's no sun on your north panels. So your maximum DC power is effectively 31/36 * 12.24 = 10.54 kW DC. Very reasonable to have on a 10 kW AC inverter, you'll have little or no clipping.

While if your roof "slope" were 0:12, then there'd be no difference, and you have the possible worst case clipping of the DC/AC ratio of 1.23. Even that wouldn't be too bad, and of course that would only be if your house was in the tropics so the sun was sometimes directly overhead.

In between, you get a blend of the two extreme cases. If you provide the roof slope, and the azimuth (how far off true south your "south" roof faces), then if I get a chance I'll do a little vector math to see if your panels could every actually produce enough power at STC to cause your inverter to clip.

Cheers, Wayne
How can I find these details for my roof?
 

SunnyInVegas

Member
Dec 2, 2020
29
9
Las Vegas, NV
If you have access to the approved plan set for the permit that was issued, then they should be printed on there somewhere. If you don't have the plan set, ask the contractor for it. When the permit is finaled, it should remain with you.

Cheers, Wayne
I think I found it on the spec sheet for my hoa.

South facing— pitch 17, azimuth 181
North facing — pitch 18, azimuth 1
 

wwhitney

Member
Nov 2, 2017
748
905
Berkeley, CA
South facing— pitch 17, azimuth 181
North facing — pitch 18, azimuth 1
OK, here's a quick first look. I'm going to simplify to 31 panels, pitch 18 degrees, azimuth 180 degrees, and 5 panels, pitch 18, azimuth 0 degrees.

I'll call Las Vegas's latitude 36.2 degrees. The earth's tilt is 23.5 degrees. So the sun will occasionally be directly perpendicular to your panels (18 > 36.2 - 23.5). Then when that's true, it will be 36 degrees off perpendicular from the 5 panels on the north. cos(36 deg) = 0.81, so effectively your 5 north panels are like 4 south panels.

That means on those occasions, your DC/AC ratio is 35/36 * (12.24 / 10) = 1.19. That's a bit worse than I expected, but your roof slope is pretty low.

A better analysis would consider how often it's true that the sun's angle is close enough to the panel normal to cause clipping. But that would require more time/interest/knowledge than I have right now. I don't think PVWatts supports multiple arrays, otherwise that would be a good solution. Not sure if there's a free multiple array PV simulator that would model the clipping issue with a common inverter.

Cheers, Wayne
 
  • Helpful
Reactions: jjrandorin

sorka

Well-Known Member
Feb 28, 2015
7,618
5,645
Merced, CA
Don't forget clouds. On partly cloudy days, I've seen my output go way higher than it can with 100% blue sky due to the extra reflected sunlight off the clouds.
 

arnolddeleon

Supporting Member
Jul 21, 2012
640
674
SF Bay Area
I'm sure @nwdiver has good thoughts on this.

My thoughts on clipping:
  • How often will it occur? If a larger inverter will cost more money will you recover that cost in extra production? Assuming you had the space on the roof, are the dollars better spent on additional panels?
  • What's the efficiency curve look like? It looks like the smaller inverter gets to peak efficiency sooner than the larger inverter. It is possible that the total energy output will work out the same. E.g. the smaller inverter captures more energy earlier and would lose some on the rare times it would clip. It might be work out the other way, the smaller inverter will capture more energy.
  • The panels will degrade and get dirty
  • Vegas is presumably hot (which lowers panel efficiency) when the sun is high and closer to the optimal angle.
 

nwdiver

Well-Known Member
Feb 17, 2013
7,432
9,441
United States
I'm sure @nwdiver has good thoughts on this.

My thoughts on clipping:
  • How often will it occur?

NREL says ~never. Oversize ratio of 1 (12.24kW inverter (math was easier)) vs Oversize ratio of 1.22 (10kW inverter)

Screen Shot 2020-12-03 at 12.22.45 AM.png

Screen Shot 2020-12-03 at 12.22.06 AM.png

Screen Shot 2020-12-03 at 12.26.50 AM.png
 
  • Informative
Reactions: arnolddeleon

wwhitney

Member
Nov 2, 2017
748
905
Berkeley, CA
NREL says ~never. Oversize ratio of 1 (12.24kW inverter (math was easier)) vs Oversize ratio of 1.22 (10kW inverter)
Nice. Did you enter it as a single array of 36 panels on the south exposure? Or is there a way to enter a system with two different array orientations?

Cheers, Wayne
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.