After a 16 month waiting period, our 2 PWs became operational yesterday! Of course I couldn’t wait to do my first simulated grid outage test which I did today. I wanted to share my results of the test so others can compare and contrast it to other forum member’s experiences. I am presently still running in Self-Powered mode with no option for TIme Based Control yet. How long does it normally take to get access to TBC and is there any way to speed that up?
When the simulated grid outage test began, the PWs were at 53 percent charged, the PV system was generating about 1 kW (lots of dark clouds this morning), and the test lasted about 10 minutes before I flipped the main breaker back on to reconnect to the grid.
1. Some LED lights flickered when the main breaker was turned off.
2. Clocks did NOT reset on kitchen appliances or any other AC powered clocks in the house.
3. No other electronic devices were affected that I observed.
4. I have several Cyberpower and APC UPS devices in the house and none of them intervened during the simulated outage.
5. I received a push notification of the outage on all of my Apple devices that have the Telsa app installed, including my Apple Watch.
6. I turned on the oven, toaster, and hair dryer to increase the house backup load to about 6 kWs with no problems except 6 below.
7. A Panasonic Inverter type microwave oven did not work the same during the outage. It seemed to run at a lower pace and it had a lower pitch hum when running. After the grid power was restored I turned it on again and it sounded normal. Does this have anything to do with the inverter technology in the oven? I also have another GE Profile built in microwave oven and that oven did not seem to run any different during the outage.
8. I flipped the main breaker back on to end the simulated outage and shortly thereafter received another push notification saying that the grid had been restored.
Should I also run another simulated outage test under different conditions to make sure everything is working as it should be working?
When the simulated grid outage test began, the PWs were at 53 percent charged, the PV system was generating about 1 kW (lots of dark clouds this morning), and the test lasted about 10 minutes before I flipped the main breaker back on to reconnect to the grid.
1. Some LED lights flickered when the main breaker was turned off.
2. Clocks did NOT reset on kitchen appliances or any other AC powered clocks in the house.
3. No other electronic devices were affected that I observed.
4. I have several Cyberpower and APC UPS devices in the house and none of them intervened during the simulated outage.
5. I received a push notification of the outage on all of my Apple devices that have the Telsa app installed, including my Apple Watch.
6. I turned on the oven, toaster, and hair dryer to increase the house backup load to about 6 kWs with no problems except 6 below.
7. A Panasonic Inverter type microwave oven did not work the same during the outage. It seemed to run at a lower pace and it had a lower pitch hum when running. After the grid power was restored I turned it on again and it sounded normal. Does this have anything to do with the inverter technology in the oven? I also have another GE Profile built in microwave oven and that oven did not seem to run any different during the outage.
8. I flipped the main breaker back on to end the simulated outage and shortly thereafter received another push notification saying that the grid had been restored.
Should I also run another simulated outage test under different conditions to make sure everything is working as it should be working?