I just had a new powerwall installed complete with new panels. My cottage is 100% off grid . My installer is having a very difficult time trying to figure out why the rate of charge is so low. He has called the Tesla support several times , has reset ample times,
And still very little solar getting through to charge powerwall. The cottage uses very little power and although a very sunny day yesterday, the powerwall charged only 1.6 KW. I have 10 new panels and 4 older ones .
I am very disappointed of course as I was really looking forward to the extra power .
Has anyone else experienced this problem or have ideas to where the problem may be stemming from?
Wow, interesting and welcome to TMC. I have yet to see one person trying to troubleshoot an off grid system by themselves, so things are a bit different. I do not think many people use Powerwalls for fully off-grid setups. Most off grid folks want a lot more control over their setup and go with Sol-Ark, Outback, or one of a couple other manufacturers.
From your initial description, it sounds like the CT meters that report the solar production to the TEG are likely not correctly configured.
A Couple pieces of information are needed:
Old panel wattage and count - What inverter?
New panel wattage and count - What inverter?
As a curiosity, what generator is used for this setup?
What is your battery percentage?
I would check both sets of CT's, or if just one set then check the CT's that measure the collective power of the PV system. It's likely that the 1.2 kW you are seeing makes sense when looking at the actual installation.
For instance, if your old PV system was 1.2 kW it sounds like the new PV system might not have any CT's.
Another possibility is that one of your PV systems are not functioning at all. Your installer should check the voltage/amperage at the 2 separate systems to see if one of them is not properly creating current.
One thing that doesn't makes sense here, is your statement about 2.5 kW for the cabin when it is vacant. Are you saying 2.5 kWh per day?
One more thing to consider is that if your total PV size is too large (5 kW AC), or your battery is too full (90-95%) or are too cold then the batteries will not charge. Check the frequency of the microgrid, and see if the TEG is limiting the PV output. If your frequency is 60 hz on the money then that isn't limiting. If your hz is above about 60.5 then the TEG is telling the modules to curtail their production.
If you have internet at the site, tell the installer to login to the Powerhub fleet view and they can look for error codes and wierdness there as well.