Typically the whole house loses power during backup operations when there is too much load for the Powerwalls to handle. They will reset the power to the home hoping to force some loads to shed. This can happens when the AC kicks on and there is no soft/hard start device installed.
If this is not the case, then there is something weird going on that may not be attributed to being close to the recommended amount of solar per Powerwall (
7.6 kW per Powerwall). First check in with your Tesla Certified installer on fixing the issue. They may have miss-configured your system, installed faulty hardware/wiring, or need to make minor adjustments for Gpez Option 1 to work. Second, Tesla may be able to remotely configure the Powerwall to coordinate solar production with your SMA inverters if your installer can not do it.
If Gpez Option 1 does not work, consider having your installer (at no additional cost to you) physically move the breakers for one of your inverters into the non-backup load panel for Gpez Option 2. In the event of grid outage, the solar inverter outside the backup gateway would automatically turn off. Not ideal, but works automatically to shed solar generation.
Ultimately your Tesla Certified installer needs to fix the system.