Newly installed 240V outlet barely too small to accept plug

Discussion in 'North America' started by Argelius, Oct 2, 2014.

  1. Argelius

    Argelius Member

    Joined:
    Jun 8, 2013
    Messages:
    239
    Location:
    Palm Springs, CA
    I just moved from IL to CA where I had a 240V outlet installed in the garage. It looks like a NEMA 14-30 outlet as pictured on Tesla's website (and is paired with a 60 AMP fuse in the fuse box).

    Screen Shot 2014-10-02 at 7.47.21 PM.jpg


    The 240V adapter on the charging cable looks like it should fit, but the bottom prong appears to be too large for the bottom hole in the outlet.

    Obviously I'll call back my electrician to take a look, but thought I'd just throw this out there to see if there's a quick fix...

    Thanks!
     
  2. Merrill

    Merrill Active Member

    Joined:
    Jan 23, 2013
    Messages:
    2,096
    Location:
    Sonoma, California
    It should be Nema 14-50 240 volt 50 amp.
     
  3. Argelius

    Argelius Member

    Joined:
    Jun 8, 2013
    Messages:
    239
    Location:
    Palm Springs, CA
    Thanks! That was helpful. I think I understand what happened now. Electrician called.

    - - - Updated - - -

    Okay. One more question. This is probably obvious, but if I just buy an adapter for a NEMA 14-30 outlet, I'm good to go (and probably much cheaper than hiring an electrician to change the outlet)?

    http://goo.gl/TDv8Po
     
  4. Lloyd

    Lloyd Active Member

    Joined:
    Jan 12, 2011
    Messages:
    4,885
    Location:
    San Luis Obispo, CA
    Umm..... the 14-30 should not have a 60 amp breaker! This is dangerous!
     
  5. Merrill

    Merrill Active Member

    Joined:
    Jan 23, 2013
    Messages:
    2,096
    Location:
    Sonoma, California
    You need to know if your curcuit breaker is a 50 amp curcuit, very important and would not recommend using an adapter. Installing the 14-50 plug should not be a big deal if you have the proper amperage curcuit.
     
  6. deonb

    deonb Active Member

    Joined:
    Mar 4, 2013
    Messages:
    3,020
    Location:
    Redmond, WA

    Yes, you'll be good to go - it will just charge slower. Probably ~14 hours for a full charge instead of ~8.

    But change out that circuit breaker like Lloyd said.

    I assume since you don't want to change out an outlet you also don't want to change out a circuit breaker. So if you get an electrician in anyway, and it's approximately the same cost, upgrade the outlet rather than downgrade the circuit breaker.
     
  7. Chris TX

    Chris TX Active Member

    Joined:
    Sep 30, 2013
    Messages:
    1,486
    Location:
    Dallas, TX
    THIS!

    Also, if the electrician put a 30A outlet on a 60A breaker/fuse, I would think twice about using them again. You also need to find out what gauge wire was used from the outlet to the fuse box. If it's rated for that 30A outlet, it's going to need to be replaced if you plan on using the proper 14-50 outlet.

    Please don't end up on the news with your garage/house/Tesla burned to the ground. You'll just make the stock price drop! ;)
     
  8. tga

    tga Active Member

    Joined:
    Apr 8, 2014
    Messages:
    2,214
    Location:
    New Hampshire
    A 14-30 outlet on a 60A breaker is dangerous, a code violation, illegal, a serious fire risk, an insurance refuse-to-pay risk, and God-knows-what-else. Was this work ever inspected? It shouldn't have passed. If you haven't paid the bill yet, I wouldn't until they fix it. If you have paid, I would demand they fix it or you will report them to the state licensing board. You need a 50A breaker, 6 gauge or heavier copper wire, and a 14-50 outlet.

    Actually, I might not let them back in my house, period. Get a real electrician who didn't find his license in a box of Cracker-Jacks.

    If you're trying to plug a 14-50 plug into a 14-30 outlet, it won't fit. That's by design, else your 50A appliance with the 14-50 plug could try to pull 50A from a 30A circuit. Attempting to do this is a fire risk, etc (see long list of bad outcomes, above).
     
  9. AoneOne

    AoneOne Member

    Joined:
    Sep 21, 2013
    Messages:
    151
    Location:
    Fox Chapel (Pittsburgh), PA
    Is it really a 60 amp breaker, or could it be paired 30 amp breakers, one for each side of the 240V circuit?
     
  10. yobigd20

    yobigd20 Well-Known Member

    Joined:
    Oct 28, 2012
    Messages:
    5,793
    Location:
    Skaneateles, NY
    THIS. wow. please call a DIFFERENT electrician because this guy clearly doesn't know what he's doing. who knows if he even used proper gauge.
     
  11. breser

    breser AutoPilot Nostradamus

    Joined:
    Aug 28, 2014
    Messages:
    2,310
    Location:
    North Bend, WA
    If it hasn't already been inspected find out who does electrical inspections in your area and get them out there (in my state you can even just ask for a general safety inspection for electrical and they'll come out and look at anything you want). They can identify if anything is done wrong and what needs to be fixed. They also have the authority to force the original electrician to fix it. I'd also suggest that you turn the breaker off and not use the outlet until you have this inspected. If the inspector doesn't think anything is wrong I'd raise the concerns about the 30A outlet and 60A breaker that have been mentioned here.

    If for some reason you live in one of the very rare areas that doesn't have electrical inspections. Then I would hire a different electrician to give their opinion on if anything was done wrong and possible to fix it.

    My overall advice is don't just trust electricians to do things correctly. Everyone makes mistakes and that's why we have inspectors. I just had some wiring in my house fixed this week that the electrical inspector noticed was wrong when he was here inspecting my work adding a 14-50 and HPWC. The work was done in 2002 and wasn't inspected (I didn't know better back then). I happened to still have the invoice and the inspector found the original electrician and made him come out and fix it at no charge to me.
     
  12. Doug Gallarda

    Doug Gallarda P03915

    Joined:
    May 6, 2013
    Messages:
    58
    Location:
    Austin, TX
  13. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    See the FAQ in this section of the board (also linked in my signature, below).

    If the breaker is marked "60", and that outlet was installed on that breaker, then as other people have said that's a giant no-no and will not protect you. Under no circumstances should you ever use an adapter with that circuit as-is because if the car - for whatever reason - decides to start charging at 40A, you will overload the outlet at a minimum. Depending upon the wire/cable used, it may be overloaded as well.

    The proper installation is linked in the document from Tesla above - a 50 amp breaker with minimum #6 Romex or #8 wire-in-conduit (smaller number is larger wire) and NEMA 14-50R receptacle. The alternate installation is a 30 amp breaker with minimum #10 wire/cable and NEMA 10-30R receptacle, paired with the correct adapter FROM TESLA - not a homemade or 14-50 to 14-30 adapter (which has some overloading risk).

    If your breaker in your "fuse panel" is labeled "30" and is a dual-handle breaker, then that's ok - you really have a 30A breaker. It's not 30+30 because the flow of current is restricted to 30 amps on either side of the electrical connection.

    We're happy to help further if you provide a picture of your breaker.
     