Plug Adapter on my Universal Mobile Connector has melted...

Discussion in 'Model S: Battery & Charging' started by joepruitt, Mar 30, 2013.

  1. joepruitt

    joepruitt Seattle Sig Red #497

    Joined:
    Oct 22, 2012
    Messages:
    27
    Location:
    Sammamish, Washington, United States
    I plugged in the ModelS today and the power ring turned red. Looked at the Universal wall connector and it was red. I tried unplugging it and replugging it in and no better. I then took the NEMA 14-50 adapter off from the cable and this is what I found.

    895228_10151571328101672_775761048_o.jpg

    I've got a 50-amp dedicated line from a single breaker into my garage so I'm only wondering if this could have been some sort of power surge. I called service today and was able to talk to a tech after hours (more awesome Tesla service) and he said he hadn't heard of this happening before.

    Meanwhile, I'm stuck in Sammamish without charging for the weekend. Luckily I have a 85kw battery so I should be good until I take it into the service center on Monday. They said they have extra cables I can swap this one out for. My main concern is a fire hazard if this happens again. Anyone have any ideas on how to troubleshoot on my end?
     
  2. mitch672

    mitch672 Active Member

    Joined:
    Jul 1, 2012
    Messages:
    1,868
    Location:
    Stoughton, MA
    I know this not the first time this has happened to a UMC, "Cinergi" (Ben) had a similar problem with his, and it needed to be replaced. By any chance have you been using 208V, more than 240V? I think some of these UMCs might have manufacturing defects where the wire connecting to the UMC socket possibly has a high resistance connection, causing the pin to heat up more, leading to an early failure of the socket...
     
  3. joepruitt

    joepruitt Seattle Sig Red #497

    Joined:
    Oct 22, 2012
    Messages:
    27
    Location:
    Sammamish, Washington, United States
    Not sure what it was using volt-wise and I can't check it now. Service did say they would replace the cable so they are covering it with the warranty. I'm more concerned with it happening again. I was an early owner so hopefully service can tell me more about the problem when I take it in on Monday.

    -Joe
     
  4. Discoducky

    Discoducky Active Member

    Joined:
    Dec 25, 2011
    Messages:
    2,884
    Location:
    Seattle
    #4 Discoducky, Mar 30, 2013
    Last edited: Mar 30, 2013
    So, we are traveling from Issaquah (right next door to Sammamish and if we were home you could use our 14-50) and are currently in Palm Springs when our UMC failed. I also saw the red ring, but my cable looks other fine than the metal locking tab at the top was pushed down and was touching the closest pin. I called 877-79-TESLA and talked to TJ who will try to get us in touch with the LA service center to get a new cable sent out Monday. Clearly they are having issues with the UMC's.

    Here's what mine currently looks like. I've bent the tab and it engages properly, but the cable still doesn't work.

    DSC08542.jpg

    Thank goodness we have had a J1772 charger within our remaining range!
     
  5. mitch672

    mitch672 Active Member

    Joined:
    Jul 1, 2012
    Messages:
    1,868
    Location:
    Stoughton, MA
    #5 mitch672, Mar 30, 2013
    Last edited: Mar 30, 2013
    Cinergi also had a very early Model S, so perhaps they've improved the UMC manufacturing already.
     
  6. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    Looks like a bit of arc'ing took place there, I hope it's a one-off. I was a bit concerned with the size of the pins on the adapter, they seem a bit small for 50A rating.

    - - - Updated - - -

    Red ring, red light on UMC, or both?

    Could be a bad receptacle / ground / etc. supplying power. I assume you've tried it at different places on different receptacles?
     
  7. cinergi

    cinergi Active Member

    Joined:
    Sep 17, 2010
    Messages:
    2,170
    Location:
    MA
    Joe -- did you swap the adapter on the end of the MC recently (e.g. to the NEMA5-15 for a 120 connection and back to the NEMA15-50)?

    Mine failed in a similar way; the material it's made out of can withstand (melt, but not start on fire) some ridiculous temperatures (I measured it -- forget the numbers I saw). It's still obviously concerning and a safety hazard (at the very least, you'll get burned touching that plug while it's charging). I'm sure they'll send yours in to the engineers like they did mine and study it.
     
  8. Discoducky

    Discoducky Active Member

    Joined:
    Dec 25, 2011
    Messages:
    2,884
    Location:
    Seattle
    Red light on UMC, 4 flashes (https://www.teslamotors.com/sites/default/files/blog_attachments/ms_mobile_connector_guide.pdf) and manual says it's lack of ground. It's also a red ring on the charge port on the car. Another outlet shows green on the UMC, but doesn't work on the car. I'm thinking about rebooting the car (center and 17" display) to see if I can get it to work.

    Another question I'd like to know if the adapter locking tab on the cable (wall outlet side) has an electrical connection? I'm assuming that it does since the UMC manual says that 5 flashes is "Sense fault circuit" which is "Make sure the Mobile Connector's adaptor is properly attached". SO if I don't get 5 flashes I'm assuming that the tab is locking properly.
     
  9. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    The sense fault circuit has to do with the UMC's detection of which adapter is there. The locking tab is not part of that, from what I have seen.

    I helped troubleshoot an issue a week ago where a NEMA 14-50 receptacle had a bad ground clasp; when you held the plug a certain way it would work but then it would stop after detecting a ground fault. I had to "adjust" the ground pin so that it would hold the ground pin effectively.

    It *could* be that there is a broken connection to the ground pin, but I'd start looking at the circuit(s) first.

    I have found that if the UMC detects a ground fault, the car will display a red ring. Fix the power problem and you'll likely get it to work.
     
  10. Daniel Scherer

    Daniel Scherer Junior Member

    Joined:
    Jan 26, 2013
    Messages:
    177
    Location:
    Monroe, Michigan, United States
    What is the yellow stuff? Was any kind of lubricant used inside the connector? I thought about putting Dielectric grease inside mine to help keep out moisture.
     
  11. Discoducky

    Discoducky Active Member

    Joined:
    Dec 25, 2011
    Messages:
    2,884
    Location:
    Seattle
    Using known good receptacles and both adaptors fit/lock properly now, the light turns green on the UMC and when connected to car does NOT lock into the car and does NOT charge. I'm currently charging from J1772 and it's nearly fully charged. I'm bummed that the UMC does NOT indicate their is an issue. I'd rather get a known good UMC to test before doing any further troubleshooting.
     
  12. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    Does the ring stay white, or turn blue, or some other color? Does the car show any indication that you've connected a charge connector?
     
  13. qwk

    qwk Model S P2681

    Joined:
    Dec 19, 2008
    Messages:
    2,817
    I had the exact same problem. Bad UMC.
     
  14. Discoducky

    Discoducky Active Member

    Joined:
    Dec 25, 2011
    Messages:
    2,884
    Location:
    Seattle
    White, no indication the UMC has been inserted. But I nearly fully charged from J1772 today.

    How long did it take to get a new one from TM? I've been told that the LA store will be calling tomorrow morning and after triage *could* overnight one from their or another close store.
     
  15. qwk

    qwk Model S P2681

    Joined:
    Dec 19, 2008
    Messages:
    2,817
    They overnighted a UMC from the service center( used), because they are on back order.
     
  16. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    Yup, failed pilot signal. Bad UMC. Good luck.
     
  17. joepruitt

    joepruitt Seattle Sig Red #497

    Joined:
    Oct 22, 2012
    Messages:
    27
    Location:
    Sammamish, Washington, United States
    Just got back from service where they replace my UMC. They looked at it right away and said it had to be replaced anyway because it was an early model and I heard something about a tech note on the 14-50 adapter. For those early sig owners out there, it might not be a bad thing to call your local service and ask them if you need to get yours replaced.

    Bottom line is that Tesla service rocks. They had me in and out in 15 minutes with a brand new UMC and adapter, tested the connection, and installed my under-display cubby that I never got on the initial delivery.

    -Joe
     
  18. Elshout

    Elshout Member

    Joined:
    Feb 3, 2013
    Messages:
    124
    Location:
    Novato
    I purposely charge at either 30 or 40 amps, never at 50 amps that that my line is capable of.
     
  19. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    This is probably the most misunderstood portion of EV charging loads and circuit capacity.

    Your branch circuit and receptacle is rated for 50 amps intermittent load. The NEC distinguishes intermittent load from continuous load, which is defined as load applied constantly for 3 hours or more. Furthermore, NEC dictates that all EV charging loads, regardless of expected charge time, are to be treated as continuous load.

    Compare an EV load, which draws a constant amount of current, to that of an electric oven or range, where the elements cycle on and off to maintain particular heat settings, or to an air conditioner unit, where the compressor cycles on and off. Because the EV charging load never cycles off until the charge is complete, there is a much greater chance for a significant heat build-up, and in some cases, a 30 amp continuous load on a 30 amp rated receptacle has resulted in complete destruction of plugs and/or receptacles.

    This is why the NEC requires the rating of branch circuit wiring, devices, and overcurrent protection to be at least 125% of the continuous load; hence the 40A charging limitation on a 50A circuit, and the 80A charging limitation on a 100A HPWC circuit.
     
  20. mknox

    mknox Well-Known Member

    Joined:
    Aug 7, 2012
    Messages:
    8,566
    Location:
    Toronto, ON
    What FlasherZ says, plus you shouldn't even be able to turn it up beyond 40 amps from the touchscreen anyway.
     