Well, then you’ll be shocked to know that this was an all day issue as the 8 hour outage caused the PV to go ON & OFF at least 10 Times during the course of the day.
I’m still not sure that we’re talking about the same thing here. If what you’re referring to is the PV going on and off as the powerwalls get charged, then no, that’s not shocking and that’s expected behavior.
If you’re saying that the PV turned on and off at least 10 times during an 8 hour outage when the powerwalls were not fully charged, then that is very unusual and definitely not expected behavior.
The PV maybe have shut off once at the start of the outage, for reasons discussed above, but then should have stayed on until the powerwalls were fully charged. If that is not what happened for you, then something is wrong.
Again, it happens. Frequently.
Multiple outages in my area resulting in all day events causing the PV to cycle On/Off a dozen times.
Again, if the PV cycling is due to the powerwalls being fully charged, then this is expected behavior and necessary. If you have multiple outages in the same day, then the PV may cycle at the beginning of each outage. But frankly, if you’re having multiple outages that frequently then you need to work with your power company to figure out what’s wrong.
Not sure if this is correct.
I believe 65Hz is the default unless you call Tesla and request it be lowered to resolve UPS issue.
Again, based on numerous posts in these forums, the frequency is 65Hz unless requested to be lowered.
If what you wrote were true, then why are there hundreds of people who have the issue with their UPS continuously during an outage when PW shuts down the PV (due to excess energy having no place to go) ?
This may need a little more investigation. I posted based on my experience, but someone else mentioned that he saw different results. Certainly from my understanding of how the system operates, and my own observations of my system, during off grid operation I don’t believe that the frequency should get any higher than 60.5 (or whatever the cut off frequency that the inverter is set to) no matter what the maximum frequency is set to on the powerwalls. But it’s possible that other systems behave differently than mine or I am misunderstanding how it works.
I’d love to see others do some tests with their systems to see what results they get.
————
Just to be clear though, I would absolutely expect your PV to cycle multiple times during an extended outage if your powerwalls are fully charged or become fully charged during the outage.
Other than that, and perhaps once at the start of the outage your PV should not cycle at all.
I was simply saying that it hardly seems worth worrying about that one potential cycle that may or may not happen at the start of the outage. But maybe I misunderstood and that’s not the only cycle that you were concerned about.