wbhokie
Member
Depends on the person you get. Some people go "by the book" and others just work their tickets if they know how.I guess I got lucky since I did not have to provide any devices to prove I needed the change.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Depends on the person you get. Some people go "by the book" and others just work their tickets if they know how.I guess I got lucky since I did not have to provide any devices to prove I needed the change.
I'm still waiting for confirmation from my request last week. How did you go about confirming the new setting?I submitted through the app and they came back asking for model numbers. However, the next day they said the change was made. They didn't tell me the freq and I never sent in my the models numbers. However, I was able to confirm they changed it to 62.5 Hz when testing it.
I don't believe there is any customer-viewable setting to see what the frequency is set to, so the only way to confirm is to take yourself off the grid when the battery is full. A few ways exist to test:I'm still waiting for confirmation from my request last week. How did you go about confirming the new setting?
I just put a kill a watt meter in the outlet, and turned off the breaker, and watched things work. Nice and easyI'm still waiting for confirmation from my request last week. How did you go about confirming the new setting?
I'm still waiting for confirmation from my request last week. How did you go about confirming the new setting?
"grid_code_overrides": [
{
"name": "soc_freq_droop_config_df_max",
"value": 2.5
}
]
Didn't notice this before, but you may be able to verify the override in the api.
https://teg/api/site_info now has this
Code:"grid_code_overrides": [ { "name": "soc_freq_droop_config_df_max", "value": 2.5 } ]
"grid_code_overrides":[
{
"name":"soc_freq_droop_config_df_max",
"value":2
}
I confirmed by API, but you will also know when you don't hear all the UPS beeping. The only way to test is by having a full PW and killing the grid.
"grid_code_overrides": [
{
"name": "soc_freq_droop_config_df_max",
"value": 2.2
}
]
grid_code_overrides: [
{
name: "soc_freq_droop_config_df_max",
value: 2,
}
],
I'll do a full test killing the grid this weekend but looks good.
How do I check and update the firmware?UPDATE on the frequency rise to 65 Hertz: After the September 23rd grid power outage event when Tesla confirmed my PW2 raised the frequency to 65.4 Hertz, I simulated the exact same event again last Sunday, October 14th with a pull to the Service Disconnect on the Main Breaker Unit.
All parameters were the same: PW2 100% charged, sun shining and solar input at 3.5-4 kW and my house was using about 1.5-2 kW at the time. All appliances remained the same. I had both the new Eaton UPS (that can pass-thru up to 70 Hertz power) and the Minuteman UPS (that can pass-thru up to 66 Hertz power) at two of my locations where critical CPU based hardware was running while the rest continued to use the previous APC and Trip-Lite UPSs.
When the Service Disconnect was pulled, all the UPSs briefly came to life and went to their internal batteries to facilitate the very short loss of 120 volt power when the Gateway relay snaps shut. But within a second or so, they all went back to using the house supplied current (now PW2 based). I was able to document via video in real-time the rise of the Hertz level from 60.0 to the maximum employed.
But THIS time, the frequency only rose to 63 Hertz. The rise took about 2-3 seconds but held steady at 63 Hertz. Thus ALL of my UPSs work with this new Hertz limit as the APC and Trip-Lites function at 63 Hertz (actually, Tesla confirmed 62.9 Hertz).
The ONLY difference between the September event and the October event was the firmware release. At the initial event I had 1.22.3 and I currently have 1.25.0. After speaking with Tesla customer tech support yesterday about this test, it was confirmed that the frequency rise is not some built-in hardware circuit on the PW2 but is actually software controlled. Version 1.25.0 differs from 1.22.3 in many more ways than the support page states - the limit on the frequency rise is one of the updates - at least against my Enphase M215 inverters as I have been able to test.
How do I check and update the firmware?
Mine was 3rd-party install and I went through Tesla directly.If my Powerwall was installed by a third-party installer, does the request need to go to them or to Tesla?
Mine was 3rd-party install and I went through Tesla directly.