My local PW and Solar PV system contractor submitted for permit to install, but was flagged down because of the Generation Meter Adapter vs Main Service Panel rating limitation per Southern California Edison:
Single Line Diagram Deficiency: Main Service Panel is 225A. For GMA MSP can be 200A or Less.
Please refer to section 5.4.1.1 of NEM Handbook.
The proposed system is as shown in the attached plan, basically:
A. 11.725 kW Solar PV (35 LG 335 panels) and 2 Powerwalls
a. 8.04 kW PV to SE7600 inverter on back up side with 2 Powerwalls, and Essential Load
b. 3.68 kW PV to SE3800 inverter with GMA
- Now, my installer wants to scrap the GMA, and reduce the solar system to 32 panels (10.72 kW) in ONE SE7600 inverter - oversizing DC/AC ratio of 1.41.
- Upgrading service to 400A is projected to cost upwards of $12K - so that is a 'no go'.
1. Are there any alternative solution to be able to keep the original plan?
Like, instead of upgrading to 400A service - can we "downgrade" to 200A to meet the GMA vs MSP limit without breaking 120% rule?
2. I asked to cut the number of panels to 30 (10.05 kW) in one SE7600 inverter (DC/AC ration 1.32) - is this better/worse than DC/AC ratio of 1.41?
All panels are on 2nd story roof oriented West at 260 degrees with 23 degree tilt, no shading, lots of sunshine with summer temp 90-110 and 30-60 dry winter in SoCal Inland Empire.
I do not know much about electrical systems at all, so any insight is welcome.
Thanks for any feedback.
RBRT
Single Line Diagram Deficiency: Main Service Panel is 225A. For GMA MSP can be 200A or Less.
Please refer to section 5.4.1.1 of NEM Handbook.
The proposed system is as shown in the attached plan, basically:
A. 11.725 kW Solar PV (35 LG 335 panels) and 2 Powerwalls
a. 8.04 kW PV to SE7600 inverter on back up side with 2 Powerwalls, and Essential Load
b. 3.68 kW PV to SE3800 inverter with GMA
- Now, my installer wants to scrap the GMA, and reduce the solar system to 32 panels (10.72 kW) in ONE SE7600 inverter - oversizing DC/AC ratio of 1.41.
- Upgrading service to 400A is projected to cost upwards of $12K - so that is a 'no go'.
1. Are there any alternative solution to be able to keep the original plan?
Like, instead of upgrading to 400A service - can we "downgrade" to 200A to meet the GMA vs MSP limit without breaking 120% rule?
2. I asked to cut the number of panels to 30 (10.05 kW) in one SE7600 inverter (DC/AC ration 1.32) - is this better/worse than DC/AC ratio of 1.41?
All panels are on 2nd story roof oriented West at 260 degrees with 23 degree tilt, no shading, lots of sunshine with summer temp 90-110 and 30-60 dry winter in SoCal Inland Empire.
I do not know much about electrical systems at all, so any insight is welcome.
Thanks for any feedback.