@FlyReaFast, To expand on operations and features, there is a "backup" "option" (it was ordered and supplied fitted as part of my original order for my region [Australia]) for the PW-2 that provides a sub-second switch-over much like or more exactly like a UPS.
In "Self-Powered" mode:
A. Grid Functioning:
1. If the battery is at the Reserve level and there is no sun, power is from the grid; if the grid fails, power comes from battery
2. As the sun comes up, solar power is supplied to the load and the grid use drops
3. As solar increases, grid power drops further and when solar exceeds load, the battery starts charging
4. This continues until the battery is full then excess solar is exported to the grid
5. If solar production is more than the load plus the battery max charge of 5 kW, excess is exported to the grid
6. If the battery is above reserve and load exceeds solar production, battery provides the difference and if needed so too will the grid
6a. If the battery is full, excess solar goes to the grid
The net result of this is that if battery is above reserve, and as the solar power generation changes, what is not taken as a load from solar goes to the battery and is taken from the battery as clouds pass by thereby maximising use of your own solar generation. It's rather cool I must say!
7. With sun and grid fail, PW-2 disconnects from grid and provides power from solar and/or battery - limit of 5 kW plus Solar
8. With no sun and grid fail, PW-2 provides power like a UPS limited to 5 kW and a sub-second switch-over
My understanding of a PW-2 overload as per items A7 or more likely A8 of 5 kW is shutdown/auto-start but I have not had this happen yet.
B. Grid Fail
1. Much like the above under grid fail conditions (A7 and A8)
2. With no grid, the PW-2 will also be able to use the Reserve value down to zero
What I don't yet know but has been asked elsewhere in this Forum (with no answer yet) is what happens if the grid is down, the battery is flat and the sun comes up? Because the Solar system needs to detect the grid (or the PW-2 as a fake grid) in order to enable power output.
It may be the PW-2 is "smart" enough to see the solar power, no load and figure it should start charging the battery until solar exceeds load but...
I also have a generator and changeover switch on my grid input (ie switch grid input to genset) which I can use to power my home/load so I figure I can use this to pretend the grid is alive. In theory I see no reason this won't work but I need to disconnect the Solar in case the battery gets full or Solar exceeds charge rate so as to avoid trying to back-feed the genset. As long as this is remembered, I could start the genset to get the system running (disconnect Solar, start genset to start PW-2, disconnect genset and connect Solar) then run from Solar/Battery but have not had to do this yet
Finally, the other "problem" I have is the genset is only rated at 3 kW so the PW-2 would most likely cause it to shutdown (overcurrent) but I figure it would run long enough to kick-start things. Next investment is a 15 kW diesel genset
Cheers,