That would be awesome. Thanks for sharing that news. MassRenewables installed my Solar system. Those guys are a little pricey but they really do excellent work.
Question: My 100 Amp Panel is pretty full. In fact when they installed the Solar they tapped the main lines coming into the panel because there was no room to back feed a breaker (or there was some other restriction of how many amps they could back feed through a breaker). It's 7.6 kW of panels on a 6 kW inverter.
If I wanted a Powerwall, would that all tie into the Solar System boxes or does that require more stuff in the main panel. It would probably only be one Powerwall.
They will run your 100A service entrance into the Powerwall "Gateway" which is like the DPST ATS that disconnects you from a grid.
On the output lugs of that they will run a new cable into your panel, and one to a new "generation" panel where they will combine together the Powerwall plus your existing PV. This will replace your existing line-side connection. There should be no busbar rating limitation (only the rating of the lugs on the gateway, which is far more than 100A as it is designed to supply 200A load panels plus generation).
FWIW the incentive will be paid by average kW discharged during a capacity event, so you could do two and get double the incentive. And two is not linearly more expensive than 1 since the overhead (generation panel, disconnect, Gateway, most of the install labor) is all the same. In fact with 6kW inverter they may even say the only way is to have two, because the Powerwall can only charge at 5kW. The MassRenewables guys are very knowledgable on this so I am sure they can walk you through it. Note that since the incentive is paid on production there is a caveat that if you do not have enough PV production you may not have charged your Powerwall enough to get full value of the incentive in a discharge event, because if you have PV and want to discharge to the grid (which you will want to do to get the full incentive) you are not allowed to charge from the grid, you can only charge from PV.
The incentive should be available without PV also, and then it is much more clear since you can charge from the grid and discharge to the grid (which you can not do with PV).