eprosenx
Active Member
Lots of good info and suggestions. Thank you. I believe the install (in wall) is 6 gauge. Because we weren’t sure at the time of install on which side of the garage we wanted the EVSE we actually ran the 25 foot section from the 14-50 plug to the EVSE in the form of a 25 foot RV 50 amp extensión cord. To be to code it had to be run in a “vented” conduit. You can actually see it in the very first picture in one of my previous posts in this thread. It was meant as a temporary measure until we determined what would be our long term EV....now determined to be the model 3. The original 14-50 install was like 250 bucks as it was a breaker, 4 feet of cable and a receptacle. We had the 50 amp extension cord as we are RVers.
We are currently at our winter home so can’t get pictures of the panel.
We’ll post what we decide to eventually do.
Thanks again.
Oh right! Canada! I missed that... So I know more about NEC than Canadian code, but mostly the baseline requirements are the same (wire gauges, etc...)
I have never heard of the "vented" conduit thing (though I do see it in Europe). So that may be a Canadian thing.
I am very much anti-extension cord for your permanent installation. More receptacles/plugs is more points for failure. I don't think extension cords are allowed ever for a permanent install in the US.
So I would advise you to either hard wire your 14-50 to the location you want it, OR just hard wire it into a Wall Connector.
P.S. I am curious how you ended up with a Tesla to J1772 adapter? Did you have a Tesla before with some different Tesla provided EVSE and wanted to charge the Leaf? Or you just have it to charge the LEAF off Tesla Destination Chargers (that makes sense).