Repurposing an electric oven 40A circuit for charging

This site may earn commission on affiliate links.
So, would adding a 50A for the NEMA 14-50R be too much for the sub-panel without repurposing the electric oven breaker

Yes, it will be okay unless you're running the electric oven and all four burners while charging the car and drying clothes all that the same time, with most lights and appliances and lights on. That assumes there's a 100A breaker in the upstream service panel -- it may be a 125A in which case I know you'll have plenty of room.

Your panel is fine in terms of capacity - the question will be the upstream breaker size in the main panel.