I found the documentation for my SolarEdge SE7600H-US
https://www.solaredge.com/sites/default/files/se_hd_wave_inverter_installation_guide_na.pdf
Appendix starts at page 78. Looking at page 81 there is a high default trip limit of 60.6 if I read this correctly ?
The other document I found is https://www.solaredge.com/sites/default/files/se-hd-wave-single-phase-inverter-datasheet-na.pdf , but is useless I think
I also found this one https://www.solaredge.com/sites/default/files/application_note_power_control_configuration.pdf
I thought the "Wakeup configuration" would help, but the tech support at powerEdge says that the values are hard coded depending on the country.
Any thoughts ?
They also go way overboard when the batteries aren't fully charged. I had the problem last month where my batteries were down to less than 5% during a 46 hour outage and the Powerwalls raised the frequency in an effort to warm up. The solar and Powerwalls were cycling all day, charging for 5 to 30 minutes before shutting down and starting the cycle over again. They upgraded the firmware on my inverters and made some changes to address the issue. They confirmed things worked fine a couple of days later during a simulated outage but the temperature was warmer and the batteries were already at a higher state of charge.No, that won't fix the issue because the PW needs to shift the frequency to curtail solar production. The problem is they go way overboard when the grid fails and the batteries are fully charged, immediately jumping to 66Hz to shut everything down. If you come up to full charge during an outage, the frequency shift is gradual and stops as soon as solar production stops. But they seem to think that to make this work with every (non-compliant) inverter in the world that they have to do this 66Hz jump when in reality there are other options like starting at 63Hz for a few seconds or ramping up in steps. But they won't fix this until as many people that are bothered by it call and complain. So please do, and voice your dissatisfaction with the current operation.
1. Correct, based on current firmware
2. Correct, Powerwall raises frequency, which triggers solar to turn off. Powerwall detects the total power through the CT meters.
3. Correct
Best solution to generation overage problem is to reduce PV generation manually, by turning off PV breakers, or increasing usage. Great time to do some baking with an electric stove, maybe turn on the AC too lol.
Best solution for the flickering lights problem is to mass email Tesla support and make them realize what a problem this is for you as a customer.
For sensitive plug in electronics that don't like 66hz, use a more expensive inverter based plug in UPS, which conditions the power automatically to 60 hz.
For other types of plug in UPS that detect 66hz as a bad grid and go to backup power, use a different UPS that allows a wider range of power frequency before tripping
We discussed this at length in that thread that Ninja mentioned above. There were a few UPS units I no longer needed due to having a powerwall now. Some of the other ones that I did still need I replaced with ones made by Eaton, which support the power frequency that the powerwalls put out during a power outage. They do work, and they don't need to last long... only long enough for the transition time between the main power to the powerwall, which is seconds at the maximum.