Lol good luck with using Qualcomm :eek:

1) hard to say as don’t know your house size or future plans for pool , AC etc

2) 14-50 you will be fine ...however you still need a 50a circuit which is half of what your panel is rated for ...ie what else do you have in panel (pic will help)

3) definitely HPWC if 2 electric cars unless you don’t mind switching plugs back and forth

4) I didn’t however my run is less than 3ft and I did to code ...ie correct conductor size ,load , conduit where needed ...height of HPWC from ground ...:oops:

I've had fairly good luck at Qualcomm, but that's likely because I only go either before 7 am or after 8 pm.

My house is ~1800 sf. We have a pool/pool pump, an electric range/oven, gas dryer, and rarely run the AC.

Here's a pic of the panel:
20180627_091056.jpg
 

Attachments

  • 20180627_091046.jpg
    20180627_091046.jpg
    375.9 KB · Views: 39
Wow looks like you will need that 200a service panel ....call SDGE and open a service order ...most likely the transformer in front of your house has the power just need to run the service line and pay an electrician to change panel