Scary issue with Nema 14-50 adapter melting

This site may earn commission on affiliate links.
If it's the same unit that was burnt by the outlet, it could easily have been damaged enough to be causing a poor connection on that side. Definitely replace it.

If you check out my pics you will see it fully melted the one terminal and also the adapter. As I said, I replaced both the outlet and the adapter, but with a Leviton outlet rated to 75C. Cord was not damaged at the adapter.
 
Last edited:
This is from another post


Please don't hack off the UMC's wall plug socket without understanding that there is a fourth control pin with the following resistance values to ground:

Tesla UMC Plugs Resistance

40 amps - 9.08k ohms

24 amps - 33.16k ohms

16 amps - 75k ohms

12 amps - 140k ohms
I'm adding this datapoint to every thread where I see this table -

32 amps - 20k ohms (measured from a Canadian 14-50 adapter)
 
  • Informative
Reactions: Rocky_H
HPWC Connector power options.JPG
 

Attachments

  • Chargnig rate kW and miles.JPG
    Chargnig rate kW and miles.JPG
    81.9 KB · Views: 884
Last night we walked into my garage and saw my NEMA adaptor, cord and outlet on FIRE!! Should I call Tesla and have them come out? I may need to call my homeowners insurance to repair my garage and fire damage. It looks like the prongs overheated and melted. Any help is appreciated.
 

Attachments

  • IMG_7588.jpg
    IMG_7588.jpg
    58.6 KB · Views: 57
  • IMG_7587.jpg
    IMG_7587.jpg
    56.9 KB · Views: 60
  • IMG_7589.jpg
    IMG_7589.jpg
    60.2 KB · Views: 63
  • IMG_7590.jpg
    IMG_7590.jpg
    58.7 KB · Views: 53
Most likely nothing to do with Tesla. Loose connection somewhere, cant tell for sure from pix, but probably owners outlet-to-UMC-plug was loose. How old was the receptacle? Daily plugging and unplugging? Residential grade receptacle or industrial grade? DIY install or electrician?
 
  • Like
Reactions: Rocky_H
have you checked the breaker? This is the device that should have tripped when too many amps go through...
No, it won’t trip in this case. There was high resistance in the connection which caused heat and it melted. Breaker will NOT trip unless it’s OVER current. If anything it was under current.

The newer mobile connectors do have temp sensors that try to catch this. Picture looks like an old Mobile Connector that should have been ditched.
 
Most likely nothing to do with Tesla. Loose connection somewhere, cant tell for sure from pix, but probably owners outlet-to-UMC-plug was loose. How old was the receptacle? Daily plugging and unplugging? Residential grade receptacle or industrial grade? DIY install or electrician?
I'd put money on the issue being either a loose wire and/or cheap 14-50 outlet. Leviton 14-50 outlets, for example, are well known to start going high resistance and melting after a few years.

This thread has the full details on which outlets are recommended for daily use:
 
  • Informative
Reactions: Rocky_H
No, it won’t trip in this case. There was high resistance in the connection which caused heat and it melted. Breaker will NOT trip unless it’s OVER current. If anything it was under current.

The newer mobile connectors do have temp sensors that try to catch this. Picture looks like an old Mobile Connector that should have been ditched.
Breaker will trip if the breaker itself is hot, generally around 140F. If the receptacle melted, I'd check the breaker. My Leviton 14-50 melted after 2 years of daily use @ 40A on my gen1 UMC. I replaced the receptacle, and a few weeks later my breaker tripped while charging. It was hot - too hot to touch. I removed and retightened the wires going into it which brought the temperatures down to around 80F.

Now even though I have a gen1 UMC, I still only charge at 32A unless I need the extra charging speed.
 
Breaker will trip if the breaker itself is hot, generally around 140F. If the receptacle melted, I'd check the breaker. My Leviton 14-50 melted after 2 years of daily use @ 40A on my gen1 UMC. I replaced the receptacle, and a few weeks later my breaker tripped while charging. It was hot - too hot to touch. I removed and retightened the wires going into it which brought the temperatures down to around 80F.

Now even though I have a gen1 UMC, I still only charge at 32A unless I need the extra charging speed.
Breakers usually have two mechanisms of tripping:
  1. Thermal trip - breaker gets too hot and it trips. Good for detecting long duration, excessive loads.
  2. Magnetic trip - too much current and it trips. Good for detecting high current under short periods of time.
Note that not all breakers include both! Check the specs on your specific breaker to confirm.

Dropping charge current a bit is very useful at reducing heat buildup - the amount of power dissipation due to resistance at a location goes up by the square of current. P = I^2 * R (P=Power, I = Current, R = Resistance) So if you drop the current by 50%, the amount of heat loss in the wires will be dropped by 75%. Going from 40 to 32A gets you 80% of the charging power, but power lost in the wires is 64% of the heat loss at 40A.

To drop the power lost in the wire by half from 40A, you would drop the charge current to about 28-29A.

I use a Gen2 Wall Connector and knowing that they are designed to handle up to 80A is nice when the car only charges at up to 48A. Just need to put it on a 100A circuit!
 
  • Informative
Reactions: Droschke
Breaker will trip if the breaker itself is hot, generally around 140F. If the receptacle melted, I'd check the breaker. My Leviton 14-50 melted after 2 years of daily use @ 40A on my gen1 UMC. I replaced the receptacle, and a few weeks later my breaker tripped while charging. It was hot - too hot to touch. I removed and retightened the wires going into it which brought the temperatures down to around 80F.

Now even though I have a gen1 UMC, I still only charge at 32A unless I need the extra charging speed.
But we were not talking about the breaker getting hot. We were talking about the outlet/plugs melting and that won’t trip the breaker.

An arc fault breaker might have tripped though.
 
Breakers usually have two mechanisms of tripping:
  1. Thermal trip - breaker gets too hot and it trips. Good for detecting long duration, excessive loads.
  2. Magnetic trip - too much current and it trips. Good for detecting high current under short periods of time.
Note that not all breakers include both! Check the specs on your specific breaker to confirm.

Dropping charge current a bit is very useful at reducing heat buildup - the amount of power dissipation due to resistance at a location goes up by the square of current. P = I^2 * R (P=Power, I = Current, R = Resistance) So if you drop the current by 50%, the amount of heat loss in the wires will be dropped by 75%. Going from 40 to 32A gets you 80% of the charging power, but power lost in the wires is 64% of the heat loss at 40A.

To drop the power lost in the wire by half from 40A, you would drop the charge current to about 28-29A.

I use a Gen2 Wall Connector and knowing that they are designed to handle up to 80A is nice when the car only charges at up to 48A. Just need to put it on a 100A circuit!
Actually that’s not quite right.

Either breaker can work. The thermal based breakers don’t work well in harsh environments and their trip point will move a lot based on ambient temp.

The magnetic ones are more immune to harsh environments and have much wider operating temp range.
 
But we were not talking about the breaker getting hot. We were talking about the outlet/plugs melting and that won’t trip the breaker.

An arc fault breaker might have tripped though.
I was correcting your statement that said the "breaker will not trip unless it was over current" which is not true. If your receptacle melted, it's worth checking the breaker as well.
 
I was correcting your statement that said the "breaker will not trip unless it was over current" which is not true. If your receptacle melted, it's worth checking the breaker as well.
The thermal breakers don't trip due to say the lugs on the breaker being loose. They don't have a thermal sensor (like on the newer Mobile connectors). However they are designed using a thermal scheme that shifts the trip point with ambient temperature. So I still stand by my statement. If a Thermal breaker had a similar fault as this plug/outlet did the results would have been similar. It would have melted down and probably not tripped or tripped far too late. They are not trying to protect against that type of fault. If a fire raises the ambient temp enough to lower the trip point enough to trip on enough load yeah. But that's not meant to be a safety feature, it's a flaw.
 
  • Funny
Reactions: Rocky_H