Self installed Tesla Wall Charger...
Discussion in 'Model S: Battery & Charging' started by HX_Guy, Dec 25, 2016.
  1. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    Took this on yesterday...pretty easy and straightforward. I thought it would be more complicated but it's basically connecting 3 wires at two ends, and popping in a breaker. Toughest part was probably inserting the wires into the charger slots, hard to see the hole and the wire are pretty stiff when that short in length.
    Started out by picking up some supplied...
    Making a hole...
    And piecing it together...pretty straight forward, though I did have to run back to Home Depot for a conduit bending tool.
    Pull the wires through...
    Mount the charger...
    Bring it up into the main panel...
    Connect to the new 60A breaker...
    And done! Well, need to paint it, but functionally done. :)
    • Like x 4
  2. Maximapolak
    Maximapolak Member
    North NJ / SouthCentral PA
    Good job. How fast are you charging at 50A?
  3. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    Is there a definite way to check? (Somewhere in the settings for last charge?)
    Off the top of my head, I was down to 77 miles and it charged to 227 miles (90%) in what showed at the beginning should take 4.5 hours...did not time it to see if that is exactly how long it took, but that comes out to 33.3 miles/hour. Its a 60A breaker by the way (48A charging).
  4. Maximapolak
    Maximapolak Member
    Right. I mean 48A.
    When it's charging, it will say on your screen how many miles per hour you're getting.
  5. shelbri
    shelbri Member
    Sandy Hook, CT
    You should install a shut off switch between the panel and the charger right next to the charger. When these are hard wired and they are in different rooms (it is required per code at least in CT) it is a good thing for safety.
  6. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    Just plugged in again and its showing 36/miles per hour.
  7. CLLACAB
    CLLACAB Member
    Simi Valley, CA
    I've been thinking about a wall charger. Can't these handle a 100 amp circuit to get 58 mph charging if you have dual chargers. Did you limit yours to 60 amps due to panel capacity?
  8. TexasEV
    TexasEV Well-Known Member
    Austin, TX
    Dual chargers are a thing of the past. Current cars have choice of either single 48A or 72A charger. He obviously chose the 48A one.
  9. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    Correct. My inventory car had the 48A charger. The 72A is optional and would use a 90A breaker.
  10. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    I did some testing and got it all nailed down...guess I could have done this testing before but now we all get to learn. :)
    The charger door will open without physically touching it by holding down the "trunk" of the remote FOB for a couple of seconds. To close it, just click once on the "roof" of the FOB, which in addition to locking the doors, also closes the charge port door.
  11. miimura
    miimura Active Member
    Los Altos, CA
    National code requires a disconnect only over 60 amps. I think he is compliant the way it is.
  12. ColdRauv
    ColdRauv Member
    Minnesota
    What size conductors did you use (and what size ground is that)?
  13. CuriousG
    CuriousG Active Member
    Elk Grove, CA
    Based on the 48A and 72A discussion, I assume you have a refreshed Model S. Why aren't you pushing the button on the HPWC to open the charge door? And the charge door should automatically close in a few seconds after unplugging.
  14. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    I wrote that reply in the wrong thread. :p
  15. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    #6 conductors and #10 ground.
  16. ColdRauv
    ColdRauv Member
    Minnesota
    Perfect. Finally, someone who sized the breaker, conductors and equipment ground correctly;):D.
    • Disagree x 1
  17. ColdRauv
    ColdRauv Member
    Minnesota
    One thing I might consider (probably too late now, however) is to move your 60A EVSE breaker away from the 60A PV breaker. Both will be plenty warm if you charge during a sunny day. They are right across from each other and the bus 'down there' will get very warm, especially with the plug-in breakers that friction-fit to the bus.
  18. HX_Guy
    HX_Guy Member
    Phoenix, AZ
    Yeah, that crossed my mind but didn't really have much choice as the rest of the bus is full and swapping with other breakers would have been a bit difficult.
    It shouldn't be an issue as I plan to charge at night, and after the battery is full, it does not matter if the charger is still connected to the car right? (As in if I plug in at night, and then do not unplug the following day after the sun is up/solar is producing).
  19. miimura
    Los Altos, CA
    If you're not charging in the afternoon, it's a non-issue.