Self-Wiring an HPWC

Discussion in 'Model S: Battery & Charging' started by RV8R, Jun 29, 2018.

  1. RV8R

    RV8R Member

    Joined:
    Apr 22, 2018
    Messages:
    48
    Location:
    Florida
    Has anyone ever attached a plug wire to the HPWC to plug into an existing outlet? Specifically I've got a generator connection to my panel through an L14-30 male receptacle, feeding in/out through a 30 Amp breaker. I understand I would not be maximizing charging ability, but could still access 240V at lower amperage. Thoughts? Thx!
     
  2. ai4px

    ai4px Member

    Joined:
    May 2, 2018
    Messages:
    273
    Location:
    Sumter SC USA
    I did it with my siemens versicharge, don't see why it wouldn't work. Neutral not needed so don't confuse neutral and ground on that round plug. Ground is needed for ground fault self test.
     
  3. RV8R

    RV8R Member

    Joined:
    Apr 22, 2018
    Messages:
    48
    Location:
    Florida
    What gauge wire did you use, and what capacity breaker was in the box?
     
  4. ewoodrick

    ewoodrick Active Member

    Joined:
    Apr 13, 2018
    Messages:
    1,085
    Location:
    Buford, GA
    If you have a plug that is a generator plug, then no, it shouldn't work, because it would be feeding the wrong side of switchover switch.

    But be aware, that while it would work if it isn't connected to a switch, then if someone does plug in the generator, then if you forget to throw the whole house breaker, you could cause, lots of damage, fire, and death.
     
  5. ai4px

    ai4px Member

    Joined:
    May 2, 2018
    Messages:
    273
    Location:
    Sumter SC USA
    Ohhh did you say MALE receptacle? That should be isolated by a transfer switch in which case, it'll have no juice on it. If you mean to plug into a generator using the female receptacle on the generator, sure.
     
  6. RV8R

    RV8R Member

    Joined:
    Apr 22, 2018
    Messages:
    48
    Location:
    Florida
    Thanks for the insight. It's not worth the risk, therefore I'll have an electrician hardwire.
     

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.