So I debated posting this on the original thread, but figured it might be too much of a derailment so I'd just start a new one. Given some recent discussions around things that might be impacted by the Powerwall's tinkering with the line frequency when the grid is down, I'm still trying to wrap my head around the WHY?
From the Powerwall lead time thread:
Now this is one thing I haven't understood, though I'd wonder if anyone on this forum could really explain it. I'm an electrical engineer, but my focus has always been on DC, I'll admit that AC circuits have a bit of 'black magic' associated with them in my mind, so there may be something I just don't understand here, but it certainly seems counter-intuitive to me. I'll ask some of my EE friends who have more background in AC systems as well.
In a DC system, there's absolutely no issue with a supply being larger than the loads it powers (we do it all the time, it's called having margin). It's true even for the bits of these Solar/Powerwall systems. Take the solar panels (DC). You can unplug the MC4 connector or turn off the disconnect switch at the inverter and the panels will be fine. Similarly you can size the panels for more power than the inverter will ever use, and you'll get clipping and some lost power that you could have gotten with a bigger inverter, but that doesn't cause any harm to the panels (in fact many people recommend this).
And then there's the Powerwall battery (DC). Again, it can provide much more instantaneous power than its 5kW inverter supports, that's not a problem for the battery (in fact higher currents do more to shorten the battery's life), it just takes longer to drain it because the inverter is the limiting factor.
And even the AC-side of the Powerwall seems to be fine with this, i.e. the Powerwall's built-in inverter can output 5kW continuous, but nothing requires that you have at least 5kW of load on the circuit for it to work, in fact if you have more than 5kW (per PW) it will likely not work because you've exceeded its output and it will probably be shutting down to protect itself. If there is a minimum load requirement for the Powerwall I haven't heard it, and I should probably be concerned as my household loads can get pretty low (<300W on a typical day), so if the Powerwall would have trouble powering my house during an outage that would kinda defeat the purpose of having it.
So why is the solar inverter any different? What is the problem with drawing less current than the inverter is capable of providing at any given moment? Is the solar inverter that poorly-designed compared to the PW's inverter, or is all this just FUD and there's no real concern with there being more solar production capability than load to consume it? I'd sure hope that Tesla isn't playing these tricks without good reason (just trying to understand what that reason really is), especially since it seems there could be risks associated with pushing the frequency as high as Powerwalls apparently can/do (temporary functionality of things like UPS and PLC devices, and I'd wonder if perhaps even safety-style risks for large/small appliances with AC motors that could end up running well above their intended/tested speeds), so if it wasn't necessary it would be better to not do it at all.
I will note that reviewing the manual/specs for my Solivia 5.2, I don't see anything indicating any minimum load requirements. I also discovered while trying to research this that gas generators do have minimum load requirements, but this appears to be more of a mechanical thing, that the engines can 'drool' or get carbon build-up when operating at light loads (they're not damaged per se, they just may require more maintenance or occasional operation at higher loads to recover), so it seems to me that this has more to do with the mechanical method they use to produce the energy, where a solar inverter should be non-mechanical DC to AC conversion, more like the Powerwall's inverter, a home UPS, or the inverters that provide AC outlets in cars and the like, none of which seem to have the same requirement/concern.
Anyone here know the real answer? Thanks!
From the Powerwall lead time thread:
It's actually more than just that. When the grid is down, there is nowhere for the power from the array to go except to the house or the batteries. If the batteries can't consume what the house isn't using, there's a problem. This is why the Powerwalls have to shut the array down if they aren't at an SoC where they can accept all the extra power.
Now this is one thing I haven't understood, though I'd wonder if anyone on this forum could really explain it. I'm an electrical engineer, but my focus has always been on DC, I'll admit that AC circuits have a bit of 'black magic' associated with them in my mind, so there may be something I just don't understand here, but it certainly seems counter-intuitive to me. I'll ask some of my EE friends who have more background in AC systems as well.
In a DC system, there's absolutely no issue with a supply being larger than the loads it powers (we do it all the time, it's called having margin). It's true even for the bits of these Solar/Powerwall systems. Take the solar panels (DC). You can unplug the MC4 connector or turn off the disconnect switch at the inverter and the panels will be fine. Similarly you can size the panels for more power than the inverter will ever use, and you'll get clipping and some lost power that you could have gotten with a bigger inverter, but that doesn't cause any harm to the panels (in fact many people recommend this).
And then there's the Powerwall battery (DC). Again, it can provide much more instantaneous power than its 5kW inverter supports, that's not a problem for the battery (in fact higher currents do more to shorten the battery's life), it just takes longer to drain it because the inverter is the limiting factor.
And even the AC-side of the Powerwall seems to be fine with this, i.e. the Powerwall's built-in inverter can output 5kW continuous, but nothing requires that you have at least 5kW of load on the circuit for it to work, in fact if you have more than 5kW (per PW) it will likely not work because you've exceeded its output and it will probably be shutting down to protect itself. If there is a minimum load requirement for the Powerwall I haven't heard it, and I should probably be concerned as my household loads can get pretty low (<300W on a typical day), so if the Powerwall would have trouble powering my house during an outage that would kinda defeat the purpose of having it.
So why is the solar inverter any different? What is the problem with drawing less current than the inverter is capable of providing at any given moment? Is the solar inverter that poorly-designed compared to the PW's inverter, or is all this just FUD and there's no real concern with there being more solar production capability than load to consume it? I'd sure hope that Tesla isn't playing these tricks without good reason (just trying to understand what that reason really is), especially since it seems there could be risks associated with pushing the frequency as high as Powerwalls apparently can/do (temporary functionality of things like UPS and PLC devices, and I'd wonder if perhaps even safety-style risks for large/small appliances with AC motors that could end up running well above their intended/tested speeds), so if it wasn't necessary it would be better to not do it at all.
I will note that reviewing the manual/specs for my Solivia 5.2, I don't see anything indicating any minimum load requirements. I also discovered while trying to research this that gas generators do have minimum load requirements, but this appears to be more of a mechanical thing, that the engines can 'drool' or get carbon build-up when operating at light loads (they're not damaged per se, they just may require more maintenance or occasional operation at higher loads to recover), so it seems to me that this has more to do with the mechanical method they use to produce the energy, where a solar inverter should be non-mechanical DC to AC conversion, more like the Powerwall's inverter, a home UPS, or the inverters that provide AC outlets in cars and the like, none of which seem to have the same requirement/concern.
Anyone here know the real answer? Thanks!