New to the forums. A lot of good information here.
I know this topic has been brought up quite a bit here but I haven't seen a solution for my issue. I prefer not to say where I live in the USA but I do have installer access to both the Tesla gateway and my two Solaredge inverters. I have 4 PW's.That's a story in itself as to why I was able to have that access, but I am the owner of the aforesaid equipment.
So as the title says, my Solaredge inverters won't come back on after 5, 10, 15 or 20 minutes when I simulate a power outage. I haven't gone longer because I figure it's a moot point. I have two SE7600H inverters with no displays. As mentioned above, I have full access to the settings for both of them through Solaredge setapp.
As for the Tesla gateway, I've tried different standards from different states, i.e. UL1741(2016/2019), IEEE1547 2014 etc. in the Tesla gateway wizard. I've also changed the frequency range on both inverters in the wakeup configuration to 59.3 to 60.5.
I've tried this at multiple charge levels from 40-80%. I understand that the PW's will shutdown the inverters around 98-99% by the PW's raising the frequency to 65hz.
I will say that the state I live in doesn't want it to work. It's automatic rapid shutdown and dc discharge even though I have 4 PW's perfectly cable of charging and sustaining my home. The standard in the Tesla gateway only exists in my state. As stated above, when using the above standards in the Tesla gateway wizard, the inverters do not discharge but do shutdown initially as intended, but will not come back on. The voltage stays around 382VDC. I have 54 320W panels. I have checked the voltage on every simulated power outage at the main breaker to ensure the PW's are not feeding back on the grid and they're not.
My question is does anyone know or can someone PM me their configuration that allows the inverters to come back on and start charging after an outage? Or tell me what settings need to be changed in the Tesla gateway and/or the inverters to get them to come back on during an outage?
I would also understand if no one want's to help as it's not what my states electrical code intended.
Thanks in advance for any information on this matter.
I know this topic has been brought up quite a bit here but I haven't seen a solution for my issue. I prefer not to say where I live in the USA but I do have installer access to both the Tesla gateway and my two Solaredge inverters. I have 4 PW's.That's a story in itself as to why I was able to have that access, but I am the owner of the aforesaid equipment.
So as the title says, my Solaredge inverters won't come back on after 5, 10, 15 or 20 minutes when I simulate a power outage. I haven't gone longer because I figure it's a moot point. I have two SE7600H inverters with no displays. As mentioned above, I have full access to the settings for both of them through Solaredge setapp.
As for the Tesla gateway, I've tried different standards from different states, i.e. UL1741(2016/2019), IEEE1547 2014 etc. in the Tesla gateway wizard. I've also changed the frequency range on both inverters in the wakeup configuration to 59.3 to 60.5.
I've tried this at multiple charge levels from 40-80%. I understand that the PW's will shutdown the inverters around 98-99% by the PW's raising the frequency to 65hz.
I will say that the state I live in doesn't want it to work. It's automatic rapid shutdown and dc discharge even though I have 4 PW's perfectly cable of charging and sustaining my home. The standard in the Tesla gateway only exists in my state. As stated above, when using the above standards in the Tesla gateway wizard, the inverters do not discharge but do shutdown initially as intended, but will not come back on. The voltage stays around 382VDC. I have 54 320W panels. I have checked the voltage on every simulated power outage at the main breaker to ensure the PW's are not feeding back on the grid and they're not.
My question is does anyone know or can someone PM me their configuration that allows the inverters to come back on and start charging after an outage? Or tell me what settings need to be changed in the Tesla gateway and/or the inverters to get them to come back on during an outage?
I would also understand if no one want's to help as it's not what my states electrical code intended.
Thanks in advance for any information on this matter.