Try to keep any extension as short as possible. Line loss will reduce the Amps you can draw without tripping the breaker.
No, current in amps is constant throughout the circuit (Kirchoff's current law). Amps at the circuit breaker = amps at the plug = amps at the car no matter how long the extension cord is.
What will happen is that the longer the extension cord is, the more voltage drop it will produce, resulting in lower voltage at the car than at the outlet. This reduces total power available for charging, and therefore reduces the charging rate.
e.g. On a dryer outlet, nominal voltage = 240V, circuit rated current = 30A, maximum continuous draw = 24A. In theoretical ideal conditions, power available at the car for charging = 240 * 24 = 5.76 kW.
With long extension cord, voltage at outlet = 236V (4V drop due to the current draw through the building wiring), voltage at car = 226V (10V drop due to 100 foot extension cord), current = 24A. Power available at the car for charging = 226 * 24 = 5.424 kW.
The reason that it works this way for the car chargers is that the chargers are
regulating the current they draw. That is an unusual operating mode when compared to other devices.
For example, an electric motor like a vacuum cleaner would behave differently. The motor is under a constant mechanical load, thus must produce an equal amount of mechanical power. A longer extension cord on the vacuum will cause the same voltage drop at the vacuum cleaner motor, reducing it's power output, which will cause it to slow down, which decreases the back-EMF, which then causes current to
increase to bring produced mechanical power back to equilibrium with the shaft load. So yes, in this case, the total current draw with the extension cord will be higher than with a short cord.