miimura
Well-Known Member
Each V3 cabinet can only draw 350kVA from the gird. They are interconnected with a DC bus that can move up to 575kW in or out of a given cabinet to reduce throttling as long as all stalls are not occupied and asking for high power. So, 16 stalls can only draw 1400kVA. 2500kVA transformers are very common, so that would be my bet.Miimura... do you think SDGE will size the transformer for the full 16 X 250kw stalls or will they size for the initial 12? I ask the question because all of the San Diego Supercharging locations have been suffering from reduced output recently and with the first instance of V3, the expectation there should be good performance above 117kw V2. What size transformer for a 12 or 16 V3 stalls?
Here is a copy of a photo taken of the cabinet rating label at the recently installed V3 site in Scotts Valley, CA.