I stopped by on Friday afternoon, and no transformer pad yet that I could see.Did you see a transformer on the pad?
Thanks for the update.I stopped by the Grand Rapids SC location again this morning. The transformer is now installed. I also chatted with the crew for a few minutes. They expect everything to be installed and functional by the end of this week. Then all they have left to do is to test everything to make sure it is functioning correctly, and then the location will come online for use. He thought the testing would be completed by some time next week. :smile: Apparently, two other Michigan locations are scheduled for installation - Cadillac and an undisclosed other location, although it was unclear if the second location might be the one already being installed in Ann Arbor, MI. I personally would love to see a SC in Lansing this year.
View attachment 84277View attachment 84278View attachment 84279View attachment 84280
Thanks for the update and photos! Glad to know this Supercharger is being powered up so quickly. This looks like a 500 kva power transformer that is being used to power 8 - 100+kw charging stalls. If you were to divide this up equally it would be an average of 62.5 KVA available per individual charging stall.... or less depending on the actual capacity of each charging stall. It would be good to find out the max rating of a single charging stall.
I agree that it would be very useful to have a Supercharger in the Lansing area and hope this is forthcoming later this year. I am in Dearborn for a few days and have been using a free Level II charger at the new Amtrack train station.
Each Supercharger Cabinet supplies 2 Supercharger Stalls. Each Cabinet can put out 135 kW of DC charging power total, but is limited to 120 kW max to a single stall (330 Amps).
With the approximate 90% efficiency of the AC to DC conversion, the max AC draw of a "135 kW" Supercharger Cabinet is about 150 kW (135kW-DC/90%=150kW-AC.
Therefore the max draw of the 4 Supercharger Cabinets is 600 kW AC. Because the power factor of the Supercharger Cabinets is almost 1.0, that is about 600 kVA. However, such a power level is an unlikely and short-lived event. Utilities have great leeway in configuring power lines and transformers at typical power levels and are not required to size for worst case power levels.
500 kVA should be fine for this 8-stall Supercharger Site!
thanks for the background. Will it also take into account the vehicle SOC and have some type of charging algorithm based on arrival times or other variables? I look forward to trying it out.
The translation is 1600 amp power service is wired with 3 sets of 500 MCM (MCM is the wire size). My guess is either: there shouldn't be 3 sets of wires or it is the wrong wire size for the amperage required for this service.
I wonder how invasive the solution to this will be...
Took some more progress photos today around 5pm, here they are!
Dropbox - 2015-06-17 GR Tesla Supercharger
- - - Updated - - -
Looks like the electrical inspection scheduled for today was completed, but did not go well: https://www.accessmygov.com/CD_PropertySearchDetails/PropertyRecordDetails?RecordKey=6e83b76c-93bd-4f85-bd88-a4ba00a78c7f&RecordKeyType=12&uid=179
Violation comment says "1600a service wired with 3 sets of 500mcm"
Can anyone translate what this might mean?
I'm presuming that the "service" referred to is the cable between the transformer and the distribution cabinet. IIRC, each cabinet can only pull 160A. So the maximum that 4 cabinets could pull would be 640A per phase. How many 500mcm cables per phase? "3 sets of 500mcm" isn't really clear because there are three phases. If you say the "3" in the quote is 3 phases, then it doesn't specify how many 500mcm cables are in each set. Clear as mud.
Thanks for the update, charperimg! When you stopped by were you able to tell if the charging cables were the new thinner, liquid cooled ones or the older, thicker ones?Took some more progress photos today around 5pm, here they are!
- - - Updated - - -
Looks like the electrical inspection scheduled for today was completed, but did not go well: https://www.accessmygov.com/CD_Prop...85-bd88-a4ba00a78c7f&RecordKeyType=12&uid=179