I've done that in the past. This time I did not bother since I had time. But this was my first experience with the low powered supercharger, so I did not really know if it should act like a 120 kW charger with just a lower limit.
It is lower powered, but you should get more than 70kW from an urban stall. The point where it starts to taper down to lower power varies by car model but should hold above 70kW until at least 70% SOC. Of course, I'm talking about California weather. Cold batteries have limited charging power.
 
  • Helpful
Reactions: Viking1
Today the site was full with 4 cars waiting. That's the first time I have had to wait there.
Once I was able to plug in I only got 54 kW. Shortly after, 3 or 4 cars left and my charge rate went up to 62 kW. Still not the 72 kW I usually get there when the site isn't that busy.
At some point charging suddenly stopped and I had to manually restart it. I noticed a few other people getting out of their cars unplugging and plugging in again, so I assume they experienced the same.
 
Today the site was full with 4 cars waiting. That's the first time I have had to wait there.
Once I was able to plug in I only got 54 kW. Shortly after, 3 or 4 cars left and my charge rate went up to 62 kW. Still not the 72 kW I usually get there when the site isn't that busy.
At some point charging suddenly stopped and I had to manually restart it. I noticed a few other people getting out of their cars unplugging and plugging in again, so I assume they experienced the same.
Perhaps the station's overall load reached the transformer limit.
For example, assuming a 1500kVA transformer running at 100% capacity, that leaves ~62kW per charger, not counting overhead/losses.
Does anyone have a photo of the transformer boilerplate?

The distribution grid in that area could also be seeing higher loads, lower voltages, or fluctuations.
 
I believe the site limit is lower than the 24 stalls * 72 kw (and losses in the chargers and transformer). It's something I have seen at pretty much all Superchargers that were at or new capacity. Once the site gets full the charge rates are dropping across the board. I believe most sites are slightly underpowered to keep cost reasonable. It makes sense for most sites where it's rate that they get full. I think all the urban charger sites are not really speed critical anyways. People use them to top off while at the mall or at a restaurant. 5 or 10 min longer really doesn't matter.
 
I believe the site limit is lower than the 24 stalls * 72 kw (and losses in the chargers and transformer). It's something I have seen at pretty much all Superchargers that were at or new capacity. Once the site gets full the charge rates are dropping across the board. I believe most sites are slightly underpowered to keep cost reasonable. It makes sense for most sites where it's rate that they get full. I think all the urban charger sites are not really speed critical anyways. People use them to top off while at the mall or at a restaurant. 5 or 10 min longer really doesn't matter.
But it's definitely speed critical if you are the guy waiting in line!
 
Perhaps the station's overall load reached the transformer limit.
For example, assuming a 1500kVA transformer running at 100% capacity, that leaves ~62kW per charger, not counting overhead/losses.
Does anyone have a photo of the transformer boilerplate?

The distribution grid in that area could also be seeing higher loads, lower voltages, or fluctuations.

Reaching the transformer limit doesn't automatically reduce the power to supercharger. Transformers are passive devices with no load limiting capabilities. The issue would be the supercharger PCS overheating or having a fault.

On a side note, I believe the transformer is 2500 kVA but I'll take a picture next time I'm in the area to confirm.
 
Reaching the transformer limit doesn't automatically reduce the power to supercharger. Transformers are passive devices with no load limiting capabilities. The issue would be the supercharger PCS overheating or having a fault.

On a side note, I believe the transformer is 2500 kVA but I'll take a picture next time I'm in the area to confirm.
I understand that, but also would expect Tesla to have properly configured the supercharging hardware to adjust power limits according to the transformer size.

If you do get a chance to photo the transformer, that would be fantastic. :cool:
 
  • Like
Reactions: David99
Anyone visit this supercharger frequently? Large chunk of stalls either have trouble sustaining charging rate (starts at 60 kW then drops to 0 and stuck < 5 kW or fluctuates up/down) or today it was stuck at 40 kW. I don't think it's just me. See some other cars charge then leave a few min later. One time I tried 4 stalls right next to each other all with same issue. Been happening for at least three weeks now. The working ones have sustained 60+ kW rates.
 
Anyone visit this supercharger frequently? Large chunk of stalls either have trouble sustaining charging rate (starts at 60 kW then drops to 0 and stuck < 5 kW or fluctuates up/down) or today it was stuck at 40 kW. I don't think it's just me. See some other cars charge then leave a few min later. One time I tried 4 stalls right next to each other all with same issue. Been happening for at least three weeks now. The working ones have sustained 60+ kW rates.

This has generally been my experience with this location on the 5 occasions that I've charged there over the last 18 months. I've never gotten anywhere near 72kW with a warmed up battery and low SOC%, but it seems like 47kW is the max it will feed my 2013 S85. It's not a huge deal for me as I've never had to wait for a stall and I take the time to shop at Target for some household items. I find that despite charging at 32-47kW, it only takes about 20-30 minutes more than I would have hoped for. However, I would skip this SuC site if I was driving through on a road-trip unless I needed a 1.5hr long break.