You have a similar situation with me where I added a Tesla array + 2 PW's to an existing home with an existing array. On the Power Gateway 2 (PG2), there is space for 6 breakers, or 2x3 240v breakers. What will happen is the following:
PG2 will contain the following:
- Breaker for existing PV array
- Breaker for AC PW2
- Breaker for AC PW+ (which will include the 3.8 kW Tesla Solar Inverter)
Your entire home will be behind the PG2 so it will know how much load your home is consuming. The app will control the PW/Tesla Solar Inverter operation into a Self-Consumption mode, where it will curtail the Tesla Solar generation to limit it to the home loads.
- Due to the way it'll be setup electrically, the existing PV, will continue to generate and potentially export during the solar day.
- At night when there is no solar, the PW will discharge to keep your home load to 0.
- During the day again, if Solar + Tesla Solar > home loads, then it will use the excess PV to charge your PW.
- If the PW hits 100% during the day before your PTO, then the Telsa solar will curtail itself to 0 unless Home Loads exceed Tesla PV + existing PV, and then the PW will kick on to discharge to keep your home load to 0. Then will recharge the PW as needed with PV only production.
Hope that helps!