OK, so most of the discussion above is now moot, as the updated regulations are now out:
Updates - Electrical
There's a new bit in the informative annex A722.4 which makes very clear that these line-voltage triggered devices don't meet 722.411.4.1(iii) .... but then there's a new 722.411.4.1(iv) which gives them free rein! Somebody's lobbying efforts paid off.
The stuff about RCDs (722.531.2) has been re-written, but I think with the exact same requirements as before, just that the requirement for 6mA DC protection is now described as an "RDC-DD complying with IEC62955".
There's also a change in 722.311.201 which I hadn't noticed in the draft changes, and which I think is now very poorly drafted. The requirement for a separate final circuit per chargepoint has gone (this is positive and gives more flexibility installing eg. a cluster of load-sharing Tesla WCs), the "no diversity" statement is gone (maybe obvious, but it was useful that it used to say so), and it now permits "manual" load curtailment, without saying what that means. Manual control by a change-over switch is sensible (and IMO was always allowed), but does this new clause permit for example a commando socket and a chargepoint side-by-side with just a notice saying only one to be used at once? Or even multiple chargepoints and a notice telling you to wind down the amps in the car if you use both at once? Or a sign saying "only charge the car when nobody's using the shower"? I don't think some of these are acceptable, but the text can be read to permit them.