Tesla HPWC Charging at Very Slow Rate

Did the developer supply insufficient power?

  • Yes

    Votes: 0 0.0%
  • No

    Votes: 0 0.0%
  • The power to the outlet will be limited if air conditioning to the condo is on.

    Votes: 1 100.0%

  • Total voters
    1

SPF

Member
Feb 20, 2015
36
2
Chicago,IL
Hi! Crowd sourcing here...Any help will be most appreciated.

I just moved into new condo where I have a deeded dedicated spot that by contract is to have a Level 2 240 V 40 Amp outlet. I had my electrician install the HPWC (The black one that has Elon's signature on it. It's about 2 years old but was new and right out of the box - received as a referral reward). At my old condo, where I still can charge as I have yet to rent the condo, I can charge via the 240 outlet at about 19m/hr. At my new place with the newly installed HPWC I am IMG_3392 2.jpeg IMG_3392 2.jpeg only charging at a rate of 7 mi/hour and as soon as I log in via the app it drops to 6mi/hr.

The Tesla Touchscreen Display won't let me go higher than 12 A when plugged in. When not plugged in, I can adjust that to 40 Amps.

Of Note: The charger is directly wired to the electrical panel in my condo (9th floor) and there is a dedicated 40 A breaker.

Any thoughts on why this is happening and how to fix it would be greatly appreciated.

Thank you!
 

Silicon Desert

Active Member
Oct 1, 2018
3,031
2,790
Sparks Nevada / GF 1
Sounds like maybe the dip switch inside the HPWC wasn't set to the proper setting to reflect your breaker size, so it's defaulting to a safe (very low) 12A.
agree. That was also my first thought. The dip switch likely was not properly set when the HPWC was installed. If it is on a 40 amp breaker, then the dip switch needs to be set to 32 amps max.
 
  • Like
Reactions: doghousePVD

Hebert

Member
Apr 28, 2019
135
124
Seattle, WA
If the electrician is going to check things, I wonder how long the run is from his breaker on the 9th floor to the parking spot. Is the wire gauge correct for the length of run and amperage?
 
  • Informative
Reactions: bhorn

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.