Tesla Listed electrician using NM-B 6/2 and configures 48A of Max charging current
Tesla lists set of electrician in their site. I am more of a DIYer with EE back ground. I was getting quotes to get an idea on the cost from these listed electicians in my area. One popular electrician has done several homes in my area and this is what he does
"If you're using 6ga THHN. wire in conduit, you're fine at 60A, but for Romex the limit is lower at 55A. Since 55A breakers are non-standard, I believe that the NEC technically allows you to upsize the breaker to 60A but that doesn't lift the actual ampacity limits of the circuit which are still dictated by the Romex at 55A peak and 44A continuous, not 48A. But the EVSE doesn't allow you to configure it for a 55A circuit, only 50A or 60A, so you have to use the lower setting of 50A anyways. But setting it to 60A peak and 48A of continuous draw is code violation and might cause some trouble down the road. Pls clarify"
- Use NM-B 6/2
- Run conduit from Main panel to point where it reached attic. In attic NM-B runs without conduit
- Uses breaker 60A.
- Configures charger at 48A
- When i asked this the below he said they installed for 3000 homes and they know what they are doing and gets in to defensive conversation. Whole conversation here. I am belive there might not be issues as NEC has some buffer but its not code.