And they're gone -- 404 page not found error on the store. Hopefully they'll be replaced with a Gen 3 version.
This reinforces my suspicion that these units were just put on the store to clear out the surplus from the Destination Charging program. That program now strives to allow site hosts to collect charging fees from users, so they need Gen3 connected stations to do that. Hopefully they will make a J1772 Gen3 version and make them available to the Destination Charging program and to the public through the Tesla online store.
 

mociaf9

Active Member
Oct 18, 2018
3,042
6,336
CA
This reinforces my suspicion that these units were just put on the store to clear out the surplus from the Destination Charging program. That program now strives to allow site hosts to collect charging fees from users, so they need Gen3 connected stations to do that. Hopefully they will make a J1772 Gen3 version and make them available to the Destination Charging program and to the public through the Tesla online store.
Hopefully with the Gen3s they'll also be able to mix and match between the Tesla connector and J1772 connector units and still be able to network them together for load balancing, which they couldn't do with the Gen2 units.
 
  • Like
Reactions: miimura
Hopefully with the Gen3s they'll also be able to mix and match between the Tesla connector and J1772 connector units and still be able to network them together for load balancing, which they couldn't do with the Gen2
My wife just bought a VW ID.4 and we want to charge it on the same circuit I previously installed to charge my Model 3. Here are a few notes on what we did and how it's working:

I upgraded the Gen 2 HPWC to a Gen 3 and bought a second Gen 3. These were installed on Jan 3, 2021. We are using the TeslaTap Mini 60A to adapt the ID.4 and are getting a full 48A/11kW charge at a peak charge rate of 43mph. The two Gen 3 units were upgraded by the electrician with the required firmware add-on to enable load sharing. This setup, using the TeslaTap Mini 60 on the ID.4, is more flexible than installing a dedicated J-1772 connector. If we decide to switch how we park the cars, we can just move the adapter to the other HPWC.

The system uses one 60A branch circuit from the garage 100A sub-panel, the same circuit I previously used for my Gen 2 HPWC. We had the units installed by a Tesla-qualified electrician (same who did our previous installation). The buss connections for the two Gen 3 HPWCs are in a J-box installed near the sub-panel with no additional circuit breaker. All connections torqued as required by Tesla. Each Gen3 HPWC has GFCI protection in-built, so no GFI required on the branch circuit. Building inspector signed off the permit the following day. The two Gen3 HPWCs are joined to my home WiFi, to receive firmware updates. However, they communicate directly with each other, not via the home WiFi for load balancing. Home WiFi is not required, though firmware updates are tedious without it. All configuration and firmware add-on and update was performed by the electrician/installer.

When the TeslaTap Mini 60 is attached, it signals the HPWC to go into "J-1772" mode (according to the instructions). After a few seconds, the Tesla HPWC shows a solid blue light indication (not green). When charging the ID.4, the lights run top to bottom just as when charging a Tesla. When jacking into the ID.4, the car's charge indicator goes from white to green, then pulses while charging. When charging is complete, the Tesla HPWC returns to a solid blue indication.

When both units are connected to vehicles and requesting full power charge, the system splits 50/50 between the two cars... 24A for each vehicle. When either of them completes charging, the other vehicle gets the full 48A. I've seen all of these configurations and it is fully automatic and seamless.

The TeslaTap Mini 60 is compact and very well made. It is a quite tight fit to the Tesla handle, and there is a note in the instructions that this will be true. It was much tighter on my old Gen 2 HPWC than on the new Gen 3, but that is likely just random. Silicone spray lubricant was helpful (I used SailKote: SailKote Marine Dry Lubricant & Coating for Sails, Rigging, Deck Hardware and more. - McLube) And we won't remove the TeslaTap Mini unless we travel long distance, so it isn't a daily chore.

There is a lock eyelet to prevent the Telsa connector from being detached from the TeslaTap Mini adapter. I intend to install a Chicago screw through this hole so we don't do this by accident (which I've done a couple of times already). And when traveling, a small lock can be installed to prevent the adapter from going missing from a destination charger.

tl;dr — This is exactly what we wanted: use our existing 60A circuit, add a second vehicle, dynamic load balancing, Tesla and non-Tesla with no special tweaking of menus in vehicles. It just works!
 
My wife just bought a VW ID.4 and we want to charge it on the same circuit I previously installed to charge my Model 3. Here are a few notes on what we did and how it's working:

I upgraded the Gen 2 HPWC to a Gen 3 and bought a second Gen 3. These were installed on Jan 3, 2021. We are using the TeslaTap Mini 60A to adapt the ID.4 and are getting a full 48A/11kW charge at a peak charge rate of 43mph. The two Gen 3 units were upgraded by the electrician with the required firmware add-on to enable load sharing. This setup, using the TeslaTap Mini 60 on the ID.4, is more flexible than installing a dedicated J-1772 connector. If we decide to switch how we park the cars, we can just move the adapter to the other HPWC.

The system uses one 60A branch circuit from the garage 100A sub-panel, the same circuit I previously used for my Gen 2 HPWC. We had the units installed by a Tesla-qualified electrician (same who did our previous installation). The buss connections for the two Gen 3 HPWCs are in a J-box installed near the sub-panel with no additional circuit breaker. All connections torqued as required by Tesla. Each Gen3 HPWC has GFCI protection in-built, so no GFI required on the branch circuit. Building inspector signed off the permit the following day. The two Gen3 HPWCs are joined to my home WiFi, to receive firmware updates. However, they communicate directly with each other, not via the home WiFi for load balancing. Home WiFi is not required, though firmware updates are tedious without it. All configuration and firmware add-on and update was performed by the electrician/installer.

When the TeslaTap Mini 60 is attached, it signals the HPWC to go into "J-1772" mode (according to the instructions). After a few seconds, the Tesla HPWC shows a solid blue light indication (not green). When charging the ID.4, the lights run top to bottom just as when charging a Tesla. When jacking into the ID.4, the car's charge indicator goes from white to green, then pulses while charging. When charging is complete, the Tesla HPWC returns to a solid blue indication.

When both units are connected to vehicles and requesting full power charge, the system splits 50/50 between the two cars... 24A for each vehicle. When either of them completes charging, the other vehicle gets the full 48A. I've seen all of these configurations and it is fully automatic and seamless.

The TeslaTap Mini 60 is compact and very well made. It is a quite tight fit to the Tesla handle, and there is a note in the instructions that this will be true. It was much tighter on my old Gen 2 HPWC than on the new Gen 3, but that is likely just random. Silicone spray lubricant was helpful (I used SailKote: SailKote Marine Dry Lubricant & Coating for Sails, Rigging, Deck Hardware and more. - McLube) And we won't remove the TeslaTap Mini unless we travel long distance, so it isn't a daily chore.

There is a lock eyelet to prevent the Telsa connector from being detached from the TeslaTap Mini adapter. I intend to install a Chicago screw through this hole so we don't do this by accident (which I've done a couple of times already). And when traveling, a small lock can be installed to prevent the adapter from going missing from a destination charger.

tl;dr — This is exactly what we wanted: use our existing 60A circuit, add a second vehicle, dynamic load balancing, Tesla and non-Tesla with no special tweaking of menus in vehicles. It just works!
Oops... The units were installed on Jan 3, 2022, last week, not 2021! Sheesh. This happens every year.
 

Rocky_H

Well-Known Member
Feb 19, 2015
7,287
8,972
Boise, ID
The buss connections for the two Gen 3 HPWCs are in a J-box installed near the sub-panel with no additional circuit breaker.
*facepalm*
All connections torqued as required by Tesla.
Sooo, you torqued as per Tesla instructions, but did not use the breaker per each wall connector as the Tesla instructions say?
The Gen2 wall connectors allowed the wire joining in a junction box like that, but the Gen3 versions don't. I am not saying there is going to be a problem with it that way, but it's not per the manufacturer's directions, which makes it a code violation, albeit a minor one.
 
*facepalm*

Sooo, you torqued as per Tesla instructions, but did not use the breaker per each wall connector as the Tesla instructions say?
The Gen2 wall connectors allowed the wire joining in a junction box like that, but the Gen3 versions don't. I am not saying there is going to be a problem with it that way, but it's not per the manufacturer's directions, which makes it a code violation, albeit a minor one.
Sigh. This was installed by a Tesla-qualified electrician. This is all they do... EV charger installs. End-users cannot install load sharing Gen 3 units as DIY — special instructions and firmware add-on is required that Tesla makes available only to qualified installers.

The J-box and buss bars is the approved way to connect all units to the same branch circuit. This is as true for the Gen 3 as it was for the Gen 2. And yes, the electrician torqued all connections as specified in the installation instructions. And there is no requirement to use a separate breaker for each unit. I asked. It's not required and adds no value.
 
  • Disagree
Reactions: Rocky_H

Sophias_dad

Active Member
Supporting Member
Jul 29, 2018
1,882
2,092
Massachusetts
special instructions and firmware add-on is required that Tesla makes available only to qualified installers.
I don't think that's correct. And page 24 of the Gen3 manual clearly says every HPWC is supposed to have its own breaker. It is therefore required, even if it doesn't add value. I suspect the reason they did it that way was to allow for different maximum currents per HPWC, which was not possible with the Gen2.
 
  • Informative
Reactions: Rocky_H
Hi @Sophias_dad, you may be misinterpreting the two pictorial examples on page 24, which are not normative requirements. There is no statement requiring breakers per unit.

The normative specification on page 24 is "Power sharing circuits may be installed in an electrical panel that supports other loads." Our power sharing circuit, we have only one 60A power sharing circuit, is installed in our 100A garage sub-panel on a single 60A breaker. That is according to specification. We have two Gen 3 HPWCs on that power sharing circuit, also matching the specification, which is four or fewer.


But most importantly, our circuit was designed by and the work was performed by a Tesla-qualified electrician according to their Tesla-specific training on installing Gen 3 HPWCs. All they do is install EV charger circuits (both residential and commercial). They have installed hundreds of them.

If others on this forum are interested in configuring a power sharing arrangement with Gen 3 HPWCs, I recommend they contact a Tesla-qualified electrician, as we did, and discuss their specific situation. This forum is not a suitable place to debate the hundreds of code requirements for high-power electrical work. Make one phone call, get all the answers you need that are relevant to you, your local code, and specific situation.
 
  • Disagree
Reactions: Rocky_H

Sophias_dad

Active Member
Supporting Member
Jul 29, 2018
1,882
2,092
Massachusetts
The normative specification on page 24 is "Power sharing circuits may be installed in an electrical panel that supports other loads." Our power sharing circuit, we have only one 60A power sharing circuit, is installed in our 100A garage sub-panel on a single 60A breaker. That is according to specification. We have two Gen 3 HPWCs on that power sharing circuit, also matching the specification, which is four or fewer.
You are misinterpreting that page, IMHO. The quote is saying "You don't need a dedicated subpanel to support one or more HPWCs, if you have the space for the breakers, you can put them in your main panel". In fact if you read the rest of that paragraph, its very clear that they DON'T want you sharing breakers between HPWCS, specifically "If space is limited or the main power supply is far from the Wall Connectors, installing a dedicated load center may be prudent". If they expect you to hang multiple HPWCs off one breaker, there would be no reason for a secondary load center(subpanel).

There's also no specification for four or fewer, unless you have a different manual than me. If you are following the pictures and getting from that that you may only have four HPWCs connected, why aren't you also following those same pictures showing every HPWC on its own dedicated breaker.

I really don't care. Maybe someday I'll call Tesla for a 'final' word from someone who is reading the exact same manual we apparently both have.
 
  • Informative
Reactions: Rocky_H
On the question of four or fewer, apologies for overstating that as a requirement, it isn't. It is however a recommendation, and a suitable upper limit for our circumstances. And we have only two wall connectors, so we are under the recommended limit. Here's how we calculated it:

Power sharing feature enables up to 16 wall connectors installed at the same site to intelligently share the site's total available power—that's a design maximum limit;
However, power sharing requires at least 6A of power per HPWC at 100% utilization;
We have 60A allocated to power sharing at our site;
We may therefore not provision more than eight HPWCs at our site.

All of this is in English on p.25, no need to look at the pictures and try to figure anything out from them.

Additionally, we are installing this system at our home, intending it for overnight charging of multiple vehicles. The table on p.25 recommends 12+ amps per HPWC at 100% utilization for 6+ hour charge time. Available current is 48A (see p.5), 48 / 12 = 4.

So we cannot practically provision more than four HPWCs to power share our 60A service for our intended use.

In our configuration—two HPWCs—our 100% utilization is 24A for each.

No need to look at the pictures to figure this out.

While this material in the manual is useful for end-purchasers to reason about their own site power and charging requirements, it is necessary to engage a licensed Tesla-qualified installer, as we did, to design and install the system. The installer will refer difficult situations to Tesla and adapt each situation to local code and to Tesla's recommendations. Best to get a site consultation before purchasing equipment to be sure your intended use can be satisfied.
 
  • Disagree
Reactions: Rocky_H

miimura

Well-Known Member
Aug 21, 2013
6,844
6,739
Los Altos, CA
I don't have a link for definitive reference, but as I recall, the current firmware only allows 4 WCs to load share today, regardless of what the manual says (16). In any case, you can set the sharing total to be greater than one maximum circuit. For example, you could share 4 WCs across a 100A sub-panel. That would allow one car to charge at 48A, two at 40A, three at 26A or four cars at 20A.
 
  • Informative
Reactions: Rocky_H

Products we're discussing on TMC...

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.