Does your UMC bear a listing mark? The UL database only shows the HPWC (FFWA.E351001) and the J1772 adapter (FFVI2.E353200). Mine isn't listed, which makes me assume that Tesla calls it part of the car.
UL 2594 (standard under which the HPWC is listed) permits cord-and-plug connected sets. Because the HPWC is shipped with terminal blocks and not a power cord, the HPWC listing doesn't include the power supply conductors and therefore is not violated when cord-and-plug is connected to it. As long as article 625 is satisfied (12 in. maximum cord length) along with all other wiring methods (proper cable clamps, etc.), then you can use the HPWC with a cord and plug set (bonus is that it qualifies as a disconnect if you can lock it
It's going to be pretty tough with a cord that big to satisfy the 12" maximum length on the cable.
I have not found any instruction which requires it to be hard-wired, which would trigger the 110.3 manufacturer's instruction clause.
Nope the UMC does not have a listing Mark.
I was surprised the plug adapters for the UMC are not listed.
Only the J1772 adapter is CE and UL component (UR) listing. I anticipate because the J1772 adapter and charge stations are electrical infrastructure and independent of any vehicle manufacture.
As for cord and plugging the HPWC, we have a difference of interpretation.
FWIW, Typically the UL Listing FFWA.E351001, UL2594 Standard and the NEC 110.3(B) requires the qualified installer to follow the EVSE manufacture installation instructions.
This is all about how the equipment was investigated and tested for the UL listing (110.2 Approval) the 1st requirement for installation by the NEC, it must be listed and just because it is a cord and plug EVSE does not dissolve the Listing requirement.
That I can see, Tesla only includes the hard wiring method in the instructions and does not provide provision for installing the HPWC with a cord and plug, hence the NEC and UL listing does not include that installation method for the Tesla HPWC.
Also, even though NEC 625 may allow for cord and plug EVSE it is still is up to the building official (AHJ) to allow/approve that installation, especially if the EVSE does not come with a cord and plug attached or a cord and plug are not part of the EVSE installation instructions.
Also, also, the current HPWC installation instruction (page 2 Warnings) do require "grounding through a permanent wiring system or an equipment grounding conductor" and cord and plug installation does meet the permanent grounding requirement for the HPWC.
Is cord and plug safe? That is a question for the EVSE manufacture and UL.
The #1 question, could the chargers/battery pack back-feed the plug when it is disconnected from the receptacle?
IMHO, hard wiring the HPWC is the best wiring method (most reliable over the long term) especially for high amperage fixed in place equipment.
As for daily charging using the UMC, irrespective of the attached adapter, repetitive plug insertion into a receptacle will degrade the contacts over time and this is why the UMC is other than the best method; as sooner or later the receptacle/plug contacts will fail and the max current usage for the plug type will have little tolerance for a weaken contact.
Should you move and the new occupant has no need for the HPWC it can be easily removed and a receptacle installed in its place or the breaker switched off and the wires terminated with wire nuts in a junction box.