The OP's slight continuous grid draw during morning solar production is a little strange. My system only shows 0.1kW to/from the grid as the system is adjusting the PowerWall charge/discharge current. Usually, the next update of the 4-circle diagram will correct itself.
On the other hand, if the CTs are not installed properly, it will make the system go haywire. In the chart below, someone came to work on my system and moved the solar CTs so that they were only measuring my SE facing array and the SW facing array was producing without being included in the Gateway's measurement. Therefore the home load was erroneously driven to zero and the SW portion of the solar was exported without the Powerwalls absorbing it. I moved the CTs (at about 1:15pm in the chart below) so that each one of the solar pair was around the wires for both solar circuits. Normal operation was restored. It started raining right after I fixed the problem, which is why the solar also dropped right after that. The system also changed to Self Powered with low reserve at 1:30pm, which reduced the PW charging to surplus solar.