Congratulations! (Doubly so on the weep holes! I had to ask nicely for them.)

I believe that you hit the nail on the head. The relevant phrase being "inhabited living space".

I can see that your electrician thinks in unistrut. Nothing is moving there!

All the best,

BG
Thanks!

Yeah not the prettiest MSP install. We had it upgraded when we bought the house a couple of years ago. The inspector had a few issues that he made the electrician fix. I had to end up scheduling the follow up inspection myself and the inspector pointed out a couple of workmanship issues that he let pass.
 
  • Like
Reactions: BGbreeder
Just following up with an update.

I haven't really heard anything from Tesla besides an automated email that my design was updated (to match the installed layout) and an email from my advisor to clarify that I had a partial home back up and two loads are not backed up which I knew and expected from my initial design back in April. My Tesla account does not reflect that the system was actually installed so I might call in a few days to make sure I'm not stuck in limbo.

Everything seems to be working as expected. The app settings initially only had the ability to set the reserve and only self powered mode as an option. But over the first week every few days another setting would show up. First, time based controls showed up, then storm watch, and finally vehicle charging when off grid. I still don't have the ability to configure the app to show the go off grid button which would be useful to manage not exporting power to the grid especially when I am not at home.

The one issue I did notice when on the roof is that several of my panels are marred. At least with the one I checked it does not seem to be actuals scratches in the glass as I could scrape the material off with my fingernail. I know this probably has minimal impact on the panel functionality but as an optical engineer in pains me to see that an optical surface was treated poorly. I didn't see the installers mishandling the panels but obviously was not watching them the whole time. Since these were probably near the last of the 340W panels it may have been these panels were out at other job sites and then returned or bottom of the barrel so to speak. Just wondering if anyone else has seen something like this.
PXL_20211018_003343386.MP_2.jpg


Only other issue which is likely a problem with my network is that I can't always connect to the gateway via the local network. I get a destination unreachable error. I have a mesh network and can see via the wifi router that the powerwall is connected and sending/receiving data. If I look at what node the gateway is connected to and reboot that node which forces the gateway to switch to a different node then I can connect but run into the problem again a few hours later.
 
Just following up with an update.

I haven't really heard anything from Tesla besides an automated email that my design was updated (to match the installed layout) and an email from my advisor to clarify that I had a partial home back up and two loads are not backed up which I knew and expected from my initial design back in April. My Tesla account does not reflect that the system was actually installed so I might call in a few days to make sure I'm not stuck in limbo.

Everything seems to be working as expected. The app settings initially only had the ability to set the reserve and only self powered mode as an option. But over the first week every few days another setting would show up. First, time based controls showed up, then storm watch, and finally vehicle charging when off grid. I still don't have the ability to configure the app to show the go off grid button which would be useful to manage not exporting power to the grid especially when I am not at home.

The one issue I did notice when on the roof is that several of my panels are marred. At least with the one I checked it does not seem to be actuals scratches in the glass as I could scrape the material off with my fingernail. I know this probably has minimal impact on the panel functionality but as an optical engineer in pains me to see that an optical surface was treated poorly. I didn't see the installers mishandling the panels but obviously was not watching them the whole time. Since these were probably near the last of the 340W panels it may have been these panels were out at other job sites and then returned or bottom of the barrel so to speak. Just wondering if anyone else has seen something like this.
View attachment 725066

Only other issue which is likely a problem with my network is that I can't always connect to the gateway via the local network. I get a destination unreachable error. I have a mesh network and can see via the wifi router that the powerwall is connected and sending/receiving data. If I look at what node the gateway is connected to and reboot that node which forces the gateway to switch to a different node then I can connect but run into the problem again a few hours later.
Did you file a complaint for your scratched panels? I just saw another thread where the customer caught it when they moved the panels to his roof. He pointed it out and they replaced the panels.

It seems like they are pretty careless moving the panels to the roof.
 
  • Like
Reactions: yblaser
Did you file a complaint for your scratched panels? I just saw another thread where the customer caught it when they moved the panels to his roof. He pointed it out and they replaced the panels.

It seems like they are pretty careless moving the panels to the roof.
Thanks for the reply and info. I haven't done anything at this point. As I said at least the couple of panels I took a close look at it was less of a scratch and more of a material transfer from whatever it was rubbed against. With a soft cloth and some elbow grease I could remove it myself.

I need to more closely inspect the rest of the panels but haven't had time. They scheduled a maintenance appointment this Thursday to verify everything is working so I could ask them then although they are probably the wrong people to address this with. Inspection is scheduled for next Monday.
 
The other thing I want to address during the maintenance visit was the air conditioner working off grid. I did connect to the gateway and used the off grid button (I don't have it in the app) and turned on the AC. It started but the house had a brown out causing lots of things to reset. I don't know if using the off grid option will cause the gateway to fall back to the grid in such a condition so should really test it with the main breaker off.
 

dailo

Member
Jul 22, 2017
773
862
Bay Area
The other thing I want to address during the maintenance visit was the air conditioner working off grid. I did connect to the gateway and used the off grid button (I don't have it in the app) and turned on the AC. It started but the house had a brown out causing lots of things to reset. I don't know if using the off grid option will cause the gateway to fall back to the grid in such a condition so should really test it with the main breaker off.
I had the same issue with my install, it is supposed to be addressed in a later software update where the Powerwall+ can handle more LRA. The LRA on my AC units were under the specs of the Powerwall+ specsheet too. I just had the maintenance crew install soft starts on my AC units and that fixed the issue.
 
  • Like
Reactions: yblaser
I had the same issue with my install, it is supposed to be addressed in a later software update where the Powerwall+ can handle more LRA. The LRA on my AC units were under the specs of the Powerwall+ specsheet too. I just had the maintenance crew install soft starts on my AC units and that fixed the issue.
Thanks. I don't have a + just two Powerwall 2s. My LRA is 117 on the nameplate. They didn't install a soft start so I'm planning on requesting one.
 
Didn't pass inspection today. The inspector had two issues.

One, in the load panels the ground bar was fastened to the enclosure with what looked to be a course threaded sheet metal screw. Since there was not three threads of engagement the enclosure wasn't grounded properly.

Second, he wanted the 125A breaker in the MSP to the gateway tied down. He said it would have been okay with just solar but with PWs it needed to be tied down. I don't know the code here but I would think with the gateway it wouldn't need to be tied down in that if the breaker was accidently pulled the gateway would prevent backfeeding. That at least seems to be with the spirit of the code.

I'm guessing it will take a couple of weeks to remedy the installation and reschedule inspection.
 

Vines

Active Member
Jul 20, 2018
2,192
2,684
Silicon Valley, CA
Didn't pass inspection today. The inspector had two issues.

One, in the load panels the ground bar was fastened to the enclosure with what looked to be a course threaded sheet metal screw. Since there was not three threads of engagement the enclosure wasn't grounded properly.

Second, he wanted the 125A breaker in the MSP to the gateway tied down. He said it would have been okay with just solar but with PWs it needed to be tied down. I don't know the code here but I would think with the gateway it wouldn't need to be tied down in that if the breaker was accidently pulled the gateway would prevent backfeeding. That at least seems to be with the spirit of the code.

I'm guessing it will take a couple of weeks to remedy the installation and reschedule inspection.
Couple things:
If the ground bar was the factory unit, its been UL listed with that panel. Mot sure why someone would replace the ground bar, but if that happened it needs to use the correct fasteners.
The 125A breaker in the MSP is not required to be fastened.
2017 NEC 705.12.B.5 specifies that you can omit the hold down breaker fastener normally required by 408.36(D) since the PV and ESS Inverter is utility interactive.
 

dailo

Member
Jul 22, 2017
773
862
Bay Area
Couple things:
If the ground bar was the factory unit, its been UL listed with that panel. Mot sure why someone would replace the ground bar, but if that happened it needs to use the correct fasteners.
The 125A breaker in the MSP is not required to be fastened.
2017 NEC 705.12.B.5 specifies that you can omit the hold down breaker fastener normally required by 408.36(D) since the PV and ESS Inverter is utility interactive.
What usually happens in these cases? Does the inspector have final say and require Tesla to install the tie down regardless?
 
Couple things:
If the ground bar was the factory unit, its been UL listed with that panel. Mot sure why someone would replace the ground bar, but if that happened it needs to use the correct fasteners.
The 125A breaker in the MSP is not required to be fastened.
2017 NEC 705.12.B.5 specifies that you can omit the hold down breaker fastener normally required by 408.36(D) since the PV and ESS Inverter is utility interactive.
Thanks. I don't think this panel comes with a ground bar. Below is an image I grabbed off the internet for the panel model. Tesla added a small (~5 position) ground bar horizontally at the bottom.

Good information regarding the hold down. Thanks!
39e92b18f5bb9db209fea107d3fe2d79d05affa9-large.png
 
  • Like
Reactions: Vines
So the second inspection didn't pass either. Tesla scheduled it for yesterday and came out early to make the fixes. They ended of tying down the breaker and replaced the fasteners on the ground bar. The inspector still was not happy with the fasteners. I wasn't there unfortunately since I thought it was going to be an easy pass so don't know the details. Here is a picture of the bar as it stands now. The old fasteners were clearly sheet metal screws and only had at most one thread of contact, but the new ones look like they are fine enough to have full engagement. I think the concern is with how many threads of engagement are into the panel itself. Oh well, I guess we'll have another go at it.

oydgi-a4MMkx7-sawBEPsc8aFNbY0oi8KVzO4kp3AmJmTb42-C9Q8vDE2AqJ76lW2hWo8R6wD0Imc_4Knca089--PbsuAm6UcNNrKx9FdWkuRS246O6RgPGp1Tb_YO2BuFYyQlFuJewTq9CQ8MGg6qQPeNqjNJqCE3FDhiVOLAr1Q8gx0up43qFZ3heSrZKv-QJVuPAYcRAjwGZtzfcGHyTI-vm5Xf3zrrkffS9zvh1IeJ7N0euEiSfVUOyvTm3C452mAsA1YW6mRrYd93yZ17h_DEyQa6CCIJ90TA8Bmf9yOXfBxcZQ96gGpJeBZAJKNSJLgVWXJe95Er_-W37AKbyl5GwoVWxjJJTc8UnVUS3xlz6BScqotEKe_RNwzH9iVzgEmH6wvJ7UO_fH7Ko5RBajVV4B37lc5huFqCpVrytDy6sx8ayGFNee2SDL1FWIFotfl99GBfoq8eRZbePVJtOUCiePyZEx-IYTRJsv5IeP-gX7bbaCC71Dlyki4E4FWKBKuP_l5iuA8lbwpMubjz7vf1Fn5hu1Z-oPG4yWKIDxxvNAgrVNe36NFo4j-sLpbF9maQk9OmsElYm7u0eYiiLWCjHI-yh2nIyuiWF-foCrSlQuiAcW-Htq1IHKXKi9kW1x6kSBSAuJG_xlZxIcStH0A3XIsMs4s4mmGFk9kKjYAnAUtkTxQ5E_keNdtIDXZKMZ4j5fyT_fZ5JmSNS0n3BaTg=w2128-h1602-no
 

Products we're discussing on TMC...

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.


SUPPORT TMC
Top