Testing 48A Charging on 40A Circuit
gavine
Petrol Head turned EV Enthusiast
Apr 1, 2014
2,553
2,091
Philadelphia, PA
I want to do this test to find out how much time it would take to trip the breaker running at 48A instead of the rated 40A.
A little background. It's a 50A breaker protecting 6AWG wire to a Tesla HPWC. I turned the HPWC up to 48A and did two tests so far, charging with the car set at 48A. Both times, I had to leave before it tripped the breaker. First time was only 30 minutes and second time was a little more than 1 hour. Temperature in the garage was around 40F both times (not sure if that matters).
I periodically felt the breaker and, even after an hour of charging, it felt "warm" at most (and my hands were cold too), It would need to get fairly hot before it trips, right?
Does anyone have any intuition as to how long it should take to trip the breaker? I figured it would not take long at all. Otherwise, I probably wouldn't have bothered doing this test in the first place.
NeverFollow
1,277
730
I am not really knowledgeable on this subject, but I did some researches for finding the correct AWG wires size fore my EVSE.
To give a quick answer, when evaluating the capacity of an electric system,
it's not just the Amperage but the estimated nominal temperature on any point of a line under load that need to be considered.
Typically you try to verify that any components of your wiring will stay up to 60 degree Centigrade under continuous load.
So a system could go up to 75 degree Centigrade to accommodate some burst,
like when an electrical motor will start without triggering a breaker all the time.
Don't take my reply as a technical and scientific answer. Consult with an electrician otherwise.
But I just wanted to give you an overall perception that I have about understanding
why a 40 A breaker don't get triggered when a particular given threshold was reached.
AWDtsla
4,262
3,952
NE
The breaker might NEVER trip, and your house could burn down in the process. It is not based on temperature, although it is obviously not immune to temperature affecting the operation of the device.
iluvmacs
487
802
Madison, WI
?? Any household breaker is designed to work by tripping when it gets hot enough inside. There are fully magnetic breakers, but they are not used residentially (and are relatively rare in commercial/industrial applications anyway).
Reactions: gavine
mongo
12,862
37,837
Michigan
A 50 A breaker with 48A load in a cold environment should not trip and even NM-B (Romex) with 65C 60C insulation is rated for 55 Amps. So, it will be a boring test assuming connections are tight.
Look up your breaker's trip curve to see the specific activation points vs temperature, time, and load.
From the QO data sheet:
Edit: corrected NM-B insulation temp
iluvmacs
487
802
Madison, WI
Your "little bit of background" didn't include why you wanted to violate the NEC and the ratings of the wire & device. How about you just put it back to the right setting and back away?
Reactions: BrokerDon
mongo
12,862
37,837
Michigan
Until the test exceeds 3 hours (NEC definition of continuous load), nothing is being violated. Longest test thus far was slightly over 1 hour.
gavine
Apr 1, 2014
2,553
2,091
Philadelphia, PA
Guys. I was monitoring the situation the entire time. The wire is protected by the 50A breaker. I just wanted to see if charging at 48A would trip the breaker quickly or not. Obviously, it didn't. I don't plan on charging at 48A normally. This was just a test. I figured the breaker and wire would at least get more than warm but they didn't.
Reactions: FlatSix911
gavine
Apr 1, 2014
2,553
2,091
Philadelphia, PA
Thank you for this. I don't drain my battery enough to allow for 3 hours of 48A charging so this test is complete.
mongo
12,862
37,837
Michigan
Wire dissipation is 44% higher at 48A than 40A, but that is still a small number.
6 AWG copper is 0.3951 mOhm per foot. At 48A, that is 0.91W per foot per conductor or 1.82W/ft for the circuit. Normal would be 1.26 W for the pair.
mongo
12,862
37,837
Michigan
Good point, but, by code is should be a 60A breaker which is why I wanted to test it. I knew it would take a while, but I didn't realize 3+ hours most likely.
Per specification, it will never trip unless the ambient temp is sufficiently above 40C.
mongo
12,862
37,837
Michigan
Dawin is about SURVIVAL of the fittest. So, by definition, winning the Darwin Award would mean I'm the fittest.
It's counter intuitive, but the Darwin Awards are for people removing themselves from the gene pool in interesting fashion.
Darwin Awards. Chlorinating The Gene Pool.
(nothing you did was actually risky (beyond the possibility of finding poor wiring the hard way) people who pop breakers in their kitchen/ bathroom are more at risk).
Reactions: Rocky_H
Evbwcaer
741
328
Minnesota
I have wondered about pulsing a charger. Just a totally random scenario, 40 amps for 1 minute, 50 amps for 30 seconds, repeat. 30 seconds is a lot shorter than 3 hours.....
I know it seems stupid to ponder, but I can imagine a scenario in the future when EV's make up over 50% of cars and renewables can generate over 100% of demand. If you''re looking at millions of cars charging just 5% faster, when the sun is blazing or the wind is blowing, it could real money and/or kWh being saved and/or not wasted.