Testing 48A Charging on 40A Circuit

mongo

Well-Known Member
May 3, 2017
12,862
37,837
Michigan
Hmmm... lots of failed breakers out there then. I've never met a breaker that could take >80% of its rating continuously overnight without tripping by morning.

There must be: Repost of QO data sheet:
breaker.PNG


It does call out free air, so in a close breaker panel with other heat sources it could trip if the enclosed space is above 40C 104F.
 

mspohr

Well-Known Member
Jul 27, 2014
8,978
10,392
California
Hmmm... lots of failed breakers out there then. I've never met a breaker that could take >80% of its rating continuously overnight without tripping by morning.
My only experience with intentionally maximum loading a breaker was at a campground in Death Valley. 30 amp breaker and I was desperate for a charge so I charged at 30 amps. Breaker was warm (so was the air) but no problems overnight. I think this was an old Zinsco breaker so I probably could have pushed it to 50 amps ;)
 
  • Informative
Reactions: nwdiver

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.