Hey guys,
While I was supercharging my vehicle yesterday, the guy at the showroom was pushing hard on the Powerwall. I tried to go through all pages of this thread, but some information seems to be outdated and in conflict of what the salesguy told me. Can I ask you guys to answer the following questions please?
I live in CA and has PG&E with the TOD rate. I have a small (1kwh) solar system in a fairly efficient house. I calculated that my system basically pays for all usage except for my AC and my car charging. Any overages are relatively low. I also live in an area with a very reliable grid, so keep that in mind when you answer the following questions.
With the powerwall, I want to see if it can do the following in order for it to make sense economically.
#1 Does the powerwall have to be installed close to the main panel? I assume the closer, the cheaper the installation is?
#2 I was told I need 2 powerwall for full power backup since 1 powerwall can only push out about 22amps. In theory, if I limit my power output. I can get away with one?
#3 Powerwall doesn't qualify for the 30% tax credit since I already have solar?
#4 Going back to #2, does that mean I need 2 to power an AC compressor let say? This leads to my next question.
#5 For it to make sense economically, I essentially need this system to shift my load off the peak period (5PM-9PM) and some partial peak time. I can do this by charging the battery with the grid during off peak hours and slowly let it out during peak time. As long as I am not creating a negative number, PG&E should just offset my bill to zero. Is that allow or possible? Last time I checked they said the firmware needs to be updated before it can happen, but I want to make sure it is actually out and PG&E will let me do this? (Peak rate is about 30 cents more expensive compare to off peak)
#6 How is the overall experience with the powerwall?
Thanks for the help.
1. The closer the PowerWall is to the main panel, the cheaper the install will be. The PowerWall itself does not have to be that close, especially if the rest of the panels and Gateway can be installed close to the main panel.
2. The installation design is limited by what can be backed up. One simple limitation is that you cannot have any single breaker backed up that is more than 30 amps per PowerWall. For example, if you want to back up an AC unit that has a 40A breaker, you need two PowerWalls. If you don't want to back up any large loads, but lots of small ones, you can probably get away with one PowerWall.
3. If you charge the batteries only from solar, you can get the 30% tax credit even if the solar is already installed. If you want to charge from the grid, you do not qualify for the tax credit.
4. Backing up the AC depends completely on how big the breaker is on it and whether it has a soft start or inverter drive.
5. PG&E EV rate Peak hours are 2pm-9pm. I have no problem using the PowerWall to drive my usage to zero during these hours. However, until there is a software update, I have to interactively change the reserve percentage to get the PowerWall to do what I want. Primarily, I want to avoid PowerWall discharge during Off-Peak, but allowing the grid to power the house during Part-Peak allows the battery to fill before 2pm and generate some Peak hour solar credits.
I noticed another fine point that was not clear to me before I looked at the behavior of my install. The power monitoring current transformers that Tesla uses to balance the house load and the PowerWall output are placed on the backup gateway in a location where it can only measure the backed up loads. Therefore, the PowerWall will not offset the usage of any loads that are not backed up. It can probably be moved, but there is a limit to how long the leads are between the Neurio monitoring device in the Gateway enclosure and the CT. I would like to add another Neurio in my main panel so that those loads can be offset as well, with a RS-485 linking it back to the Gateway. However, I'm pretty sure this is not currently supported. My reason for bringing this up is that if you left your AC outside the Gateway so that it is not backed up, its usage would also not be offset by the PowerWall. If I had AC, that would be a big problem for me. As it is, the primary loads outside my Gateway are my EVSEs and I would never want to charge the cars from the PowerWall energy anyway.