My system has been running for a few months, awaiting PTO from Xcel energy. Telsa has come back and said that Xcel has requested a transformer upgrade and that will be at my own cost. They have suggested that I replace one of my Powerwall+ with a Powerwall 2.1 and that my production will not be affected at all. However I am confused about this - how does this setup reduce the amount of energy sent to the grid but not affect my home system?
This is from Tesla:
So my question: is there any downside to me going from 2 x powerwall+ to 1 x powerwall+ and 1 x powerwall 2.1?
This is from Tesla:
"We have two options:
1. Keep the installed design and go through the transformer upgrade process. This could take 6-12 months and would be at your expense. The cost is unknown at this point. Usually, Xcel requires $1000 to complete the transformer upgrade.
2. Redesign to (1) Powerwall+ and (1) 3.8 + AC Powerwall to avoid upgrading the transformer. This would not affect the production of the system.
It would be a matter of lowering the backfeed into the utility grid. Not the in-feed to the home. This is all tied to the inverter and the AC rating of the system. If we use two Powerwall+ the AC inverter rating becomes higher than what the current transformer could support in terms of the backfeed whereas if we redesign the system to reduce the DC size to 11.6KW and AC rating to below the requisite threshold per the utility company we can proceed with the install. The reduction is in the backfeed to the utility company; not the feed into the home"
So my question: is there any downside to me going from 2 x powerwall+ to 1 x powerwall+ and 1 x powerwall 2.1?