eprosenx
Active Member
Thanks for the follow up --- I went ahead and uploaded a closer view of the panel labels/breakers- Electrical panels -
To follow up on your points----
1) You bring up an interesting point about the tandem breaker on the upper left. I will wait for the next electrician to come and ask them to see. I do want to bring your attention to the BOTTOM RIGHT tandem that is in there right now --- When the electrician took it out, he told me that the back of the break was "cut" to make it fit. It all sounds so shady with the current arrangement, am I better off to have the electrician replace all breakers to the appropriate ones? Esp after reading that label able using only correct breakers for the panel on the label itself..
2) Is it better to add a sub panel or increase the size of the panel? Considering your last point, it is very likely I will need a minimum of 2 condensers for my AC. Also, not sure if this matter, per the electrician who looked at the condenser connections -- he told me that the connections are 110V. Does that change anything?
Yeah, so this raises even more eyebrows for me.
I don't know how there are tandems in the upper left position. Did someone defeat a locking mechanism on those too? I can't tell what brand they are even. If the label on the door panel is correct, that position should not allow tandems.
If you are comfortable (and can safely) take the cover off and take some more pictures I would be curious what the bus bars for the one empty spot looks like (as well as the wiring in the rest of the panel). I wanted to make sure the panel was not like installed upside down from the label and so the *top* six positions may be valid for tandems? Also good to make sure there are not more questionable things lurking other than the hodge podge of breakers. I have not installed any of these GE 1/2in breakers before so I am curious how they connect to the bus bar.
What needs to happen is a load calculation needs to be run on the home (including the new AC units you plan to install) to figure out if you have any remaining capacity to use for a car charger. 100a may be tight. Fitting into a 100a service will save you a bunch of money though if you can do it.
By my math, if the two AC units you want to install are 120v only then you may be golden (this means the breakers are only single wide breakers rather than taking two spots each). With consolidating some circuits onto tandems (or in this case 1/2 in wide breakers) plus the one empty spot you have, this will give you a place for a single 240v breaker plus two new 120v breakers for AC plus one remaining single wide breaker position (or just don't upgrade one tandem location to a tandem yet). You might need to play a bit of musical chairs with your breakers though since like GFCI breakers don't generally come in tandem forms.
As far as the breakers go: I am sketched out by the random various breakers used and the fact that a notch mechanism was defeated. While some breakers not listed on the panel door may later have been rated for that panel (after it was produced), I am wondering if that is not what is going on here. I am guessing someone grabbed whatever they had laying around.
Since these are all (but maybe one) basic old school breakers (not AFCI, GFCI, etc...), I might heavily consider what you suggest and just buy all new breakers. They are a handful of bucks each.
If you can fit everything inside this single panel I would go with that rather than a subpanel. I personally think it is cleaner. Replacing the entire panel with one with 40 spots may not be horrible either (though again, cheapest may be to stick with what you have). The panels really don't cost that much. Labor is the spendy part. That may also set you up to be able to switch to a 200a service in the future if needs dictate it.