Nah I'll replace the wire not a big deal. I'm still waiting for the electrician to take care of it though he said he's "researching it"The simple fix, to be safe, is to replace the 60A breaker with one rated for 50A.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Nah I'll replace the wire not a big deal. I'm still waiting for the electrician to take care of it though he said he's "researching it"The simple fix, to be safe, is to replace the 60A breaker with one rated for 50A.
i.e. he's trying to figure out a way to get out of fixing his mistake once you pointed out the code to him!Nah I'll replace the wire not a big deal. I'm still waiting for the electrician to take care of it though he said he's "researching it"
Maybe. Its a short run it will be easy for me to replace. He did a nice job everywhere trenching it out to my garage 100' away I'm not mad he probably just doesn't know. it's another $100 for me to buy the 6/2 MC thhn.i.e. he's trying to figure out a way to get out of fixing his mistake once you pointed out the code to him!
You consider 100' a short run? I could be wrong, but you would be buying 6 AWG THHN per wire, by the foot. It's not like Romex where it's 6/2, 6/3. Copper wire is crazy expensive now. In CA, 6 AWG THHN is over $1.50 per foot. If you have a 100' run, that's two hots at $1.50 per foot and then 100' ground wire, that doesn't necessarily need to be 6 AWG. Still, just for two hot wires at 100', that's $300 alone.Maybe. Its a short run it will be easy for me to replace. He did a nice job everywhere trenching it out to my garage 100' away I'm not mad he probably just doesn't know. it's another $100 for me to buy the 6/2 MC thhn.
No 100' was awg 2 for the 100 amp panel. The 25' from the panel to the charger is $100.You consider 100' a short run? I could be wrong, but you would be buying 6 AWG THHN per wire, by the foot. It's not like Romex where it's 6/2, 6/3. Copper wire is crazy expensive now. In CA, 6 AWG THHN is over $1.50 per foot. If you have a 100' run, that's two hots at $1.50 per foot and then 100' ground wire, that doesn't necessarily need to be 6 AWG. Still, just for two hot wires at 100', that's $300 alone.
You could do all that, or buy a $10 50amp breaker and be done with it.
Ok got it. If you used a licensed electrician and he used Romex for a 60 amp circuit, he should re-do the wiring with THHN for free, or at least just the difference in cost between the Romex and THHN. He shouldn’t charge you for the labor.No 100' was awg 2 for the 100 amp panel. The 25' from the panel to the charger is $100.
It was $4k for the 200 or so feet from my panel to the garage and the new panel and an extra 6-50 outlet on my wife's side.
I did use one it's just most still don't know the difference as proved by multiple threads.Ok got it. If you used a licensed electrician and he used Romex for a 60 amp circuit, he should re-do the wiring with THHN for free, or at least just the difference in cost between the Romex and THHN. He shouldn’t charge you for the labor.
That’s the reason for using a licensed/insured electrician. If they make a mistake, they should make it right on their dime since you’re paying them to do it right.
You’re too nice, if you’re a licensed electrician you should know the difference between NM Romex and THHN and when/where Romex can be used. If you hired a handyman I’d be more understanding.I did use one it's just most still don't know the difference as proved by multiple threads.
Hey I liked the kid and I'm not a dick honestly romex would be fine even for 48 amps in my install. It's still thhn in Romex it's just some bs rule to account for every situation.
It's still early I'm waiting for him to do the right thing.You’re too nice, if you’re a licensed electrician you should know the difference between NM Romex and THHN and when/where Romex can be used. If you hired a handyman I’d be more understanding.
I had a 50 amp circuit installed last week for a wall charger by an electrician. I researched prior to getting it installed and after 30 mins of Googling even I learned that you can’t use NM Romex for a 60 amp circuit. After looking at the estimate from the electrician I went with, I saw he had 8 AWG THHN, not Romex for a 50 amp circuit. Even though Romex would have been acceptable for the 50 amp circuit, I feel safer having the THHN separated.
You wouldn’t be a dick if you asked him to fix his mistake. It’s ok, we all make mistakes and you can be nice and still be adamant he fix his error.
I agree - that’s why you hire a licensed electrician and that’s their job. LIke @Kairide said, you don’t have to be a jerk about it. Hopefully he comes back and fixes his mistake without you having to push further.You’re too nice, if you’re a licensed electrician you should know the difference between NM Romex and THHN and when/where Romex can be used. If you hired a handyman I’d be more understanding.
I had a 50 amp circuit installed last week for a wall charger by an electrician. I researched prior to getting it installed and after 30 mins of Googling even I learned that you can’t use NM Romex for a 60 amp circuit. After looking at the estimate from the electrician I went with, I saw he had 8 AWG THHN, not Romex for a 50 amp circuit. Even though Romex would have been acceptable for the 50 amp circuit, I feel safer having the THHN separated.
You wouldn’t be a dick if you asked him to fix his mistake. It’s ok, we all make mistakes and you can be nice and still be adamant he fix his error.
I agree I see a ton of setups on here done the same way. I don't think electricians have caught up with EV requirements. They're still using the upsize rule with the 55amp Romex.I agree - that’s why you hire a licensed electrician and that’s their job. LIke @Kairide said, you don’t have to be a jerk about it. Hopefully he comes back and fixes his mistake without you having to push further.
How is the cable run? Is it in the wall, in conduit or just stapled to the wall? A lot of NM cable is actually THHN encased in the PVC sheath so he may be Able to salvage the wires, depending.
My understanding of the rationale is that the PVC has a lower melting Point than the nylon and it also serves prevent heat insulation. If you have THHN in MC the metal conduit more effectively dissipates the heat. Note that there are fill requirements/limits on EMC, it’s not like THHN gets a ‘free pass,’ either.I agree I see a ton of setups on here done the same way. I don't think electricians have caught up with EV requirements. They're still using the upsize rule with the 55amp Romex.
It's just secured to the concrete blocks. And yeah mine is THHN in the PVC. Which is the funny part logically exposed Romex sitting on cool cinderblocks should be able to dissipate more heat then the same THHN in a hot enclosed conduit. I still want it done to code just saying In my opinion I don't think this setup poses any fire risk vs a MC or conduit THHN 6-2. If this were an in wall in attic garage install I would say that it's risky.
Yeah I do like the idea of it being in MC though it comes out of the top of my panel so it's at least 6' in the air up and over the garage door and down to the middle. MC can get crushed though and you don't know the state of the wire inside.My understanding of the rationale is that the PVC has a lower melting Point than the nylon and it also serves prevent heat insulation. If you have THHN in MC the metal conduit more effectively dissipates the heat. Note that there are fill requirements/limits on EMC, it’s not like THHN gets a ‘free pass,’ either.
I’d also note that code doesn’t allow for bare NM cable on walls ‘where susceptible to damage.’ That’s a bit vague and dependent on your inspector. My inspector said it had to be in conduit even though it was up by the ceiling.
That should work and is the same spot I had my gen 3 installed. If I ever get another electic car I will just daisy chain another gen 3 and power share off the same 60amp circuit. I used 6/3 MC in case I ever wanted to install a 14-50 outlet and paid the same price for 60 ft of it. You should be able to get 48amps out of that charger. My installer put the wire on the inside of the wall so it doesn't show.Sorry this could have been redundant since I have shared this somewhere. My electrician used these products and installed the Gen3 in our garage
If an electrician does the install you won't be able to do that - NEC requires that each EV charging circuit be separate. You can have a sub panel with two brach circuits off of it for each EV, though.That should work and is the same spot I had my gen 3 installed. If I ever get another electic car I will just daisy chain another gen 3 and power share off the same 60amp circuit. I used 6/3 MC in case I ever wanted to install a 14-50 outlet and paid the same price for 60 ft of it. You should be able to get 48amps out of that charger. My installer put the wire on the inside of the wall so it doesn't show.
That would have previously been the case, now each Gen3 Wall Connector would need to be on it's own circuit breaker. This could involve separate wire runs from the service panel or from a sub panel. You can use the Tesla automatic load sharing when more than one Gen3 Wall Connector is installed. With a 60 amp breaker and a sub panel a single Gen3 Wall Connector could charge at 48A. Two Gen3 Wall Connectors could charge at the same time, 24A each or set up so that the total charging amperage does not exceed 48A, i.e. 32A and 16A.If I ever get another electic car I will just daisy chain another gen 3 and power share off the same 60amp circuit.
Ok Just so I understand this correctly. I can't just tie two gen 3 wall chargers to the same 60amp circuit even though they would never both use more than 48amp combined. Why is this??That would have previously been the case, now each Gen3 Wall Connector would need to be on it's own circuit breaker. This could involve separate wire runs from the service panel or from a sub panel. You can use the Tesla automatic load sharing when more than one Gen3 Wall Connector is installed. With a 60 amp breaker and a sub panel a single Gen3 Wall Connector could charge at 48A. Two Gen3 Wall Connectors could charge at the same time, 24A each or set up so that the total charging amperage does not exceed 48A, i.e. 32A and 16A.
Now:
Circuit: (60A breaker)===WC-A (Charges at 48A)
Future:
............Sub Panel (60A breaker)=
..............................................................|| (60A breaker)==WC-A (Charges at 48A/24A if both WC are in use at the same time)
..............................................................|| (60A breaker)==WC-B (Charges at 48A/24A if both WC are in use at the same time)
Would have to see photos but it would seem so.On the garage wall so the run to each gen3 is short?