you may need to have a disconnect box beside the charger for the 60A. That's how it is for my area anyway.

Interesting. I was going to say that page 7 of the installation instructions says "NOTE: External disconnect switches are neither required nor recommended", then I saw that you were in Canada. Maybe it's different up there



Pop quiz: where in the US can you drive South and end up in Canada?
 
Please be careful with blindly accepting that, I’d want to get the electrician to say he used 4 awg wire, unless that’s clearly documented on your receipt.
6 awg îs fine for the 48 amp continuous of the Wall Connector. Our city specifically allows it for a direct connect since the device cannot pull more than those amps. 6awg thhn is fine and even recommended by Tesla for the Wall Connector unless some area requires a larger gauge wire.
 
My friend had a v3 charger installed and commissioned for maximum power output (11kW / 48 amps). The documentation recommended a 60 amp circuit, but the electrician only had a 50 amp breaker. He charged his car at full power for many hours before the electrician returned and replaced the 50 amp breaker with a 60 amp breaker. The 50 amp breaker never tripped (it only saw 48 amps). This is not a recommendation, just information. The wire was properly sized for a 60 amps circuit.
 
My friend had a v3 charger installed and commissioned for maximum power output (11kW / 48 amps). The documentation recommended a 60 amp circuit, but the electrician only had a 50 amp breaker. He charged his car at full power for many hours before the electrician returned and replaced the 50 amp breaker with a 60 amp breaker. The 50 amp breaker never tripped (it only saw 48 amps). This is not a recommendation, just information. The wire was properly sized for a 60 amps circuit.
Most breakers are designed to handle 80% of their peak amperage rating on a continuous basis. So a 50A breaker is designed to handle 40A of continuous current as is required while charging an EV. I’m surprised the breaker didn’t trip. I recommend not installing and using a 50A breaker for a 60A circuit, even if the draw is only 48A.
 
Most breakers are designed to handle 80% of their peak amperage rating on a continuous basis. So a 50A breaker is designed to handle 40A of continuous current as is required while charging an EV. I’m surprised the breaker didn’t trip. I recommend not installing and using a 50A breaker for a 60A circuit, even if the draw is only 48A.
Not to split hairs, but breakers are designed to handle 100% of their rated current continuously per the UL standards. But the NEC calls for 80% derating for continuous loads. Again, I'm just telling a story here about my friends experience, not making a recommendation.
 
  • Like
Reactions: doghousePVD
Not to split hairs, but breakers are designed to handle 100% of their rated current continuously per the UL standards. But the NEC calls for 80% derating for continuous loads. Again, I'm just telling a story here about my friends experience, not making a recommendation.
Yeah, I think NEC derates wires and breakers to account for potentially operating at a temperature above the design ambient range that has an upper edge of 86 deg F.