Active Member
There is one limitation which must be honored in newer panels and that is the Maximum per Stab rating of the labeling in the panel indicates that limit. Even my electrician didn't know what that meant. If you look in the panel you will see a larger breaker at the top (for some reason in Canada they put it at the bottom) and coming down from it on are two parallel bus bars. These bars have tabs attached to then which run horizontally spanning both bus bars. These are the stabs. The breakers have fingers that plug onto them when the breaker is pushed into place. Each stab will take two thick breakers - one on either side of the panel - or 4 on the slim style ones. The usual limitation is 200 A per stab. This means you can't put a 120A two pole (for a sub panel) on the left side of the panel and a 90 Amp 2 pole breaker for a HPWC on the right on the same stab. This should not be at issue in the vast majority of installations.To be clear, it's not simply a matter of enough physical space in the panel, nor totalling the ratings of all the branch breakers.
A sort of general rule of thumb seems to be that the breakers in a panel are about 2.2 times the main breaker size. Thus a 200 amp panel would typically have 440 amps worth of breakers plugged into it. But that's for a typical home. A home with a 90A circuit for charging a Tesla is not, as yet, typical. In my case the panel to which I am adding the wall charger is a 200 A panel. It already has about 1200 amps worth of breakers in it and my electrician says no problem adding a 90 Amp circuit to that. Why? Because I can document that the maximum current I have ever drawn from that panel is 122 amps. This includes times when the car is charging at 40 amps. Putting in another 90 Amp breaker will bring the total breakers in that panel to 1290 amps but as I will never charge from the 50 amp circuit (14-50R) at the same time as I am charging from the HPWC I know that it is very unlikely I'll ever see a load greater than 122 - 40 + 72 = 154 A. So I'm leaving the 14-50R in as backup as many of you here have done or are planning to do.You're supposed to do a load calculation, which includes a certain amount for lighting per square foot, derating factors for appliances, etc. A modest sized new home with 200A service and gas heat, hot water, dryer, and range could easily have headroom for a 100A HPWC.
And be sure that you get a good one who has been at it for a long time and really knows the inspectors and the local as well as the NEC codes because what we are planning to do here might be in violation of some local code where you are. I was, for example, forced, in another jurisdiction (Quebec), to put in 600A service for a house at which I have never drawn more than 180 A.You need to get an electrician in to be sure.