WC 3rd gen wiring question

Discussion in 'Model 3: Battery & Charging' started by Fat_daddy78, Jun 1, 2020.

  1. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    Just ordered a 3rd gen Wall Connector. Grabbed a 60a breaker but am hearing different opinions on the wire size. I know Tesla said to use 6 gauge at least to get it's full potential. Problem is, I have a pretty long run to my garage from my secondary panel. Will I have to much drop at 60'-70' to achieve 48 amps at the charger using 6/3 Romex? Or would that still provide max power?
     
  2. UncleCreepy

    UncleCreepy Member

    Joined:
    Mar 29, 2020
    Messages:
    164
    Location:
    Lunenburg, ON
    #2 UncleCreepy, Jun 1, 2020
    Last edited: Jun 1, 2020
    With 6 AWG, 70 ft cable length and 48 A you'll get the following results:

    Voltage drop: 2.65
    Voltage drop percentage: 1.11%
    Voltage at the end: 237.35

    That's the voltage drop from the cable only. There will be more wiring from the sub panel to the charger and lastly, there is the cable on the charger which gets quite warm at 48 A.
    If it's within your budget, I'd run a thicker cable. I use a 1/0 AWG ACWU cable between the main and the sub panel. It's less expensive than a copper cable with similar characteristics.
     
  3. paulk

    paulk Member

    Joined:
    Jan 26, 2019
    Messages:
    88
    Location:
    hartford, ct
    Romex 6/3 is only rated for 55 amps, individual wires (THWN) in conduit is rated for 65 amps and can get a bit hotter before failure. If it’s a long but simple wire run you should use the biggest wire you can for future expansion and to avoid voltage drop. I had run 2/0 gauge aluminum, which doesn’t even closely fit into the lugs, and had to use a box to change the wire to 3 gauge copper for my gen 2 wall connector. It was a pain to run, but I figured it’s future proof. A year later we got a second Tesla and I was able to share the wire with another gen 2, easy.

    If you don’t care about future proofing, you should probably use 4 gauge Romex in a wall space or 6 gauge THWN/THHN in conduit.

    Also, you don’t need 3 conductor wire for a wall connector, it only uses two conductors and a ground. That said, I would still run 3 conductors in case a future wall connector uses it.
     
    • Informative x 3
  4. Rocky_H

    Rocky_H Well-Known Member

    Joined:
    Feb 19, 2015
    Messages:
    5,809
    Location:
    Boise, ID
    Seconding what @paulk said, 6 gauge Romex is not allowed for a 60A circuit. But beyond just taking people's opinions on the internet, here is a chart of the ampacity ratings for various wire sizes and types:
    Ampacity Charts - Cerrowire

    That first column is for NM-B, which is Romex, and you can see that the 6 gauge line is only allowed for 55A.

    For the next thing, if it were just 5 or 10 feet, sure, whatever, run the fourth unneeded wire--not much cost difference. But for the 70-80 feet you are talking about, that's a noticeable waste of money, and I wouldn't do that if you still have the choice in buying materials at this point.
     
    • Informative x 1
  5. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    Doesn't sound like much of a drop in voltage, I wonder how that affects the amperage.
     
  6. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    I can only dream of adding a second Tesla at this point !
    But I'd love to "Be Prepared"
     
  7. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    Appreciate that, I thought the 6g did the job...
    Yeah I definitely want to have all the power I can. Unfortunately it is like 35 feet through joists in basement, then through basement concrete wall or band board to attached garage and another 30 feet or so on the basement wall. Not sure if I need conduit there yet. I have gray conduit around my other garage outlets.
     
  8. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    Thanks all!
    Guess I better get searching for some heavier wire.
    I had the 6/3 to do a 14-50 (much shorter ) for my camper, my original intent was to use that as well.
     
  9. Sophias_dad

    Sophias_dad Supporting Member

    Joined:
    Jul 29, 2018
    Messages:
    908
    Location:
    Massachusetts
    The amperage would still be 48, but the power delivered would be dropped by that same 1.11%... essentially nothing.

    And as you have been told, the max you can get out of the 6/3 romex for EV use is 44 amps continuously. Unless you really NEED that extra charging speed, just set the Gen3 to 40amps(or 44 if that's an option)
     
    • Informative x 1
  10. Rocky_H

    Rocky_H Well-Known Member

    Joined:
    Feb 19, 2015
    Messages:
    5,809
    Location:
    Boise, ID
    You always have the choices. You can still use the 6 gauge, but it will just need to be set down to a 50A circuit, not a 60A circuit. That's still 40A continuous supply to the car, and that's still pretty fast charging for at home.
     
    • Informative x 1
  11. Sophias_dad

    Sophias_dad Supporting Member

    Joined:
    Jul 29, 2018
    Messages:
    908
    Location:
    Massachusetts
    You might find its cheaper to run two 6 gauge conductors and smaller ground in conduit than to get 4/3 or (4/2 if it exists!) romex.

    Note that none of these(wires or conduits) need to be run through joists.. they can be face-stapled(assuming other rules about exposed romex are followed). I found 6/2 romex to be fairly easy to work with, being flat.
     
    • Informative x 1
  12. Sophias_dad

    Sophias_dad Supporting Member

    Joined:
    Jul 29, 2018
    Messages:
    908
    Location:
    Massachusetts
    Just to clarify my own statement... face stapling is allowed for 8/3 or 6/2 or larger cables... anything less is expected to be drilled through the wood. Obviously if the wire isn't crossing the wood it should be stapled to the side(regardless of size) far enough from the edges that a nail or screw won't be likely to hit it(usually the middle, but if you are dealing with a 2x10, the middle isn't necessary!)
     
  13. Rocky_H

    Rocky_H Well-Known Member

    Joined:
    Feb 19, 2015
    Messages:
    5,809
    Location:
    Boise, ID
    I don't have a citation for this, but I thought Romex was never allowed to be just attached exposed on the surface of a wall. I thought it could be by itself inside a wall, or in a ceiling or crawlspace, but but if you are going to run it along a wall's surface, I thought that needed conduit then.
     
  14. SilverString

    SilverString Member

    Joined:
    Mar 29, 2020
    Messages:
    256
    Location:
    Bee Cave, Texas
    that's not much loss current will likely remain at 48 amps, it surely will not go higher. My 240v often runs at 247v on off peak hours and the car will cut the HPWC down to a 47 amp charge
     
  15. Sophias_dad

    Sophias_dad Supporting Member

    Joined:
    Jul 29, 2018
    Messages:
    908
    Location:
    Massachusetts
    Yes, I think its gotta be 7 feet off the floor, and about half of mine is in utility space while the other half is above a drop-ceiling(all above 7 feet)
     
  16. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    Thanks for the added info. I've been looking into 4 awg thhn that's sold by the foot at the big box stores. I think I might grab that today if they have it still.

    * On a side note, I haven't got alerts to the newest replies for some reason, I wasn't ignoring them.
    Guess I probably need to adjust my notifications somewhere next
     
  17. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    oh, and yes. I want the fastest possible charge. I drive a lot. 100 miles just to/ from work daily, and much more regularly. I hope this car holds up. I already have 2,600 miles on her!
     
  18. Fat_daddy78

    Fat_daddy78 Member

    Joined:
    May 4, 2020
    Messages:
    11
    Location:
    Petoskey, Michigan
    There's many times I'm only home for a few hours so I need to make the most of it in charging
     
  19. tij664

    tij664 Member

    Joined:
    May 8, 2017
    Messages:
    247
    Location:
    Turlock, CA
    1D783C34-ED8C-4343-BEBA-54A58788516E.jpeg BE01FB83-F705-4C7E-A9CB-6718FAE9BF88.jpeg I had a short run (4 ft) but I ended up using individual THHN 6 AWG wires rated for 55 A continuous inside 3/4 EMT. I figured 48 A should be no issue for that wire. 7E83C251-CC0D-47BA-ADC4-0364406609D7.jpeg
     
    • Informative x 1
  20. gfunkdave

    gfunkdave Member

    Joined:
    Aug 10, 2016
    Messages:
    120
    Location:
    Portland, ME
    It's not about your feelings on the matter. 6 AWG THHN/THWN is good to 65A at the 75C rating, which you probably would use because your circuit breakers are probably rated to 75C.

    Furthermore, three 6 AWG wires in a 3/4" conduit is about 28% fill, which is allowed. So regardless of what you figure, it is an OK installation. :)
     
    • Like x 1

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.