'whole home backup' confusion

This site may earn commission on affiliate links.
I recently had a system installed (16kW, 2PW+, backup gateway 2) and all of my paperwork references 'whole home backup'. Basically, they pulled all of my loads from my main panel into a subpanel connected to the gateway. The only breaker in my main panel now is a 100A going to the gateway. What's odd to me is that they had me upgrade my main panel and service (which required significant trenching and $$$) from 100A to 200A, but they're only feeding this subpanel (which is capable of 225A) with 100A. There are several new loads I'd like to add in the coming months (EV chargers, electric dryer, water heater), which my project advisor was aware of, but there doesn't seem to be the bandwidth to support these in the subpanel. Am I mistaken? Should I ask Tesla to update the wiring/breaker to 200A?

My understanding (which may be wrong!) is that in order to be powered by my PV system or PWs when the grid is out, loads would need to be in the subpanel as no electricity would flow to the main.

I've included the wiring diagram below. Any insight would be much appreciated.

Thanks!


n91ktoodr6i71.png
 
They did get that right. But the scrimping on materials is contrary to the approved plans, so I'd be inclined to tell them their install isn't done until they provide the proper 200A feeders.

Cheers, Wayne
Well the change to 100A was an on-the-fly change at the time of install, where they called in and cleared it with an engineer, and I verbally approved at the time. The revised plans show the 3 AWG.

I should be fine with a 100A limit and can re-run thicker wires and bigger breakers if I ever need to. But I feel a lot better now that you've also blessed the 3 AWG - thanks.
 
Upvote 0
My plans as submitted for permit showed 4 AWG with 100A breaker, but the city properly called them on it and required a change to 3 AWG.
Oddly enough, whether that is correct depends on the size of your service. If the service is 100A (upstream most breaker), then #4 is fine for a 100A circuit. While if it is larger than 100A, #3 is required.

This is the result of two NEC rules: the first is that for most common residential service sizes, the service conductors only have to be sized at 83% of nominal. The reasons for this are a little unclear, it may be a recognition that the NEC's load calculations are particularly conservative for residences. Or it may be related to the fact that conductor ampacities are based on 3 current carrying conductors, but a 120/240V supply has only 2 current carrying conductors (in this context, the neutral is not counted, as it only carries the unbalanced current; i.e. you can't get 100A simultaneously on all 3 conductors.)

That rule means that a 100A residential service only has to be #4 Cu, not #3 Cu. And there is another rule that says a feeder never has to be larger that the service conductors.

A side effect of all this is that performing a service upgrade could require downsizing some feeder breakers for feeders that no longer get to take advantage of the 83% factor.

Cheers, Wayne
 
Upvote 0
It's crazy they put 100A source into the gateway on a home with a 200A main panel service. The gateway 2 supports 200A source input, 200A output to the backup panel, and the optional internal panel board can support 200A with 6 spaces with 125A breaker in each spot. The only reason I can think of to do this is cost savings on breakers and wires hoping no one notices or cares. See the specs here:
Tesla even shows how a 400A service can be split into two 200A systems: see bottom of this page

 
Upvote 0
Just an update that Tesla finally sent an electrician to our house to scope things out and has agreed to update the wiring & breaker to the subpanel! The fix will be scheduled for some time next week. If, for some reason, it doesn't happen I will post about the experience here. Otherwise, I'm grateful to Tesla for resolving this issue.
OK so they halfway addressed my issue today. They upgraded the breaker and wiring running from the main panel to the gateway to 200A. However, the breaker feeding the subpanel is still 100A. There were 2 reasons they said they couldn't upgrade the breaker to the subpanel. The first reason was that the permits that were approved were for a 100A subpanel. The second reason was that if I add additional loads to the backup panel, the batteries could become overloaded and automatically shut down.

The permitting issue seems like it would easily be addressed and I don't think it would prevent my own electrician from upgrading that breaker if I asked. As to the second issue, they asked me to call in to discuss adding additional loads with the engineers, so I'm trying to make that happen.
 
Upvote 0
OK so they halfway addressed my issue today. They upgraded the breaker and wiring running from the main panel to the gateway to 200A. However, the breaker feeding the subpanel is still 100A. There were 2 reasons they said they couldn't upgrade the breaker to the subpanel. The first reason was that the permits that were approved were for a 100A subpanel. The second reason was that if I add additional loads to the backup panel, the batteries could become overloaded and automatically shut down.

The permitting issue seems like it would easily be addressed and I don't think it would prevent my own electrician from upgrading that breaker if I asked. As to the second issue, they asked me to call in to discuss adding additional loads with the engineers, so I'm trying to make that happen.

At least it seems to be moving in the right direction. Your permits already call for 100amp breaker from main panel to gateway. If you change it out to 200amp, wouldn't that call for a repermit already? For my project, my advisor said any changes in the breaker size would need to go through design and permit stage again.

This is my timeline so far:
9/7-8: Solar + powerwall install. They installed a 110a breaker from main panel to gateway. My plans called for 100a breaker but they didn't have any on them.

Email - Talked with my advisor afterwards trying to get everything updated to 200a

9/16: Another crew came back to switch out the 110a breaker to 100a. They had no idea I was talking to my advisor to get it updated. They looked at my main panel and gateway and said everything can support 200a, but they don't have the breaker sizes with them. The largest one they had 125a, so they ended up using that for now.
They also noticed that the distribution panel that the first crew installed only supports 125a main and 100a loads. So if I were to upgrade to 200a, they need to switch out that panel. Also, I had 125a going from that panel to my subpanel which exceeds the rating of the panel, so they swapped that out to 100a. The subpanel needs to be switched out to support 200a main and 125a loads.

Email - Told my advisor about the changes and waiting on 3.5 weeks with no response now.
 
  • Like
Reactions: Vines
Upvote 0
If the gateway is rated for 200A, how can it be fed by 200A from the grid and 50A X 2 for the powerwalls/solar (300A total)?
The rules for installing the Gateway require a maximum 200A breaker at all the locations that could otherwise cause more than 200A to flow through the Gateway.

For example, the Gateway has 2 sets of lugs for connection on the backup side of the internal disconnect.. You could connect a load panelboard to one set of lugs, and a generation (Powerwalls/PV) panelboard to the other set. If your load panelboard were a 300A panelboard, you could indeed draw 300A through the Gateway in the above scenario and overload that double set of lugs.

But the load panelboard is limited to 200A, with a 200A main breaker in it, to ensure that no more than 200A flows out of the Gateway to that panelboard. That 200A could come all from the grid, or 100A from the grid and 100A from the generation panel, or any combination in between, but the total current through the Gateway is limited to 200A.

Cheers, Wayne
 
  • Informative
Reactions: BGbreeder and jhn_
Upvote 0
Update on my project:
City inspection happened 2 months after the install and passed with the 125a breakers. I expressed my concerns with the Tesla inspection team and they put in a request with the internal hotline to get my project upgraded to 200a.
3 weeks later an electrical team came out and upgraded everything to 200a (main panel -> gateway, gateway -> new distribution center)

Took months of back and forth with Tesla over the phone but eventually everything worked out!

Side note: The Tesla design team actually had 200a plans for my project 2 weeks after my install. But for some reason they never submitted to the city for inspection. However everyone at Tesla saw the latest 200a plans and I think kept rejecting my requests to 200a since that is what they saw already.
- The inspection team came onsite with the 200a plans
- When they called the internal hotline, the rep said my project was already at 200a until the inspection team corrected them with pictures of what is currently installed
- When I called in, several project advisors already noted that I have 200a and was confused why I was requesting an upgrade
 
Upvote 0
Now that my export cap issue is resolved, I'm going to resume pressing them on this one. I plan to try to work with their designers to incorporate my plans for additional loads/circuits into the backup. My electrician can upgrade the break to the backup panel to 200A and add the loads that I want, but I just want to get Tesla's blessing that they system can handle it.
 
Upvote 0
All, Having read these posts, I went and checked my plans and what was installed by Sunrun and found I do have a 200A installation, (when my home was built in 1997 it had the 200A panel). I have attached a copy of the plans for your inspection.
I am pretty happy with the installation that Sunrun did. Being an Electronics Technician, I was very interested in what they were doing during the install and watched the process from start to end.
 

Attachments

  • Screenshot 2022-01-03 182807.png
    Screenshot 2022-01-03 182807.png
    156.7 KB · Views: 632
Upvote 0
All, Having read these posts, I went and checked my plans and what was installed by Sunrun and found I do have a 200A installation, (when my home was built in 1997 it had the 200A panel). I have attached a copy of the plans for your inspection.
I am pretty happy with the installation that Sunrun did. Being an Electronics Technician, I was very interested in what they were doing during the install and watched the process from start to end.
You didn't include the whole diagram but your backup system appears to be limited to a 100A connection at the MSP.

There is no reason why this is an issue, just thought I'd point it out. This is a perfectly reasonable partial backup design.
 
Upvote 0
All, Having read these posts, I went and checked my plans and what was installed by Sunrun and found I do have a 200A installation, (when my home was built in 1997 it had the 200A panel). I have attached a copy of the plans for your inspection.
I am pretty happy with the installation that Sunrun did. Being an Electronics Technician, I was very interested in what they were doing during the install and watched the process from start to end.


I don't understand why Sunrun bonds neutral to ground at the Gateway, but vines and wwhitney always bond at the MSP. Like... which is better? My money is on Vines (ps, my system was installed by Sunrun).
 
Upvote 0
I don't understand why Sunrun bonds neutral to ground at the Gateway, but vines and wwhitney always bond at the MSP. Like... which is better? My money is on Vines (ps, my system was installed by Sunrun).
There should be only one location per service where neutral and ground are bonded together. Every combo meter/main panel installed should have this and it is often not removable, especially in newer panels.

It seems like an error in the CAD to show another Main Bonding Jumper (MBJ) in the GW, if in fact one already exists in the service. If you open the Gateway you should not see the large green wire inside connecting the neutral to ground. Every Gateway comes with this wire pre-installed but the installer is supposed to remove it when the service panel already has the MBJ.

On the other hand, if the Gateway is used as a service panel, such as an installation with an East Coast style separate meter socket only, then the gateway does need the main bonding jumper installed inside it.
 
Upvote 0
There should be only one location per service where neutral and ground are bonded together. Every combo meter/main panel installed should have this and it is often not removable, especially in newer panels.

It seems like an error in the CAD to show another Main Bonding Jumper (MBJ) in the GW, if in fact one already exists in the service. If you open the Gateway you should not see the large green wire inside connecting the neutral to ground. Every Gateway comes with this wire pre-installed but the installer is supposed to remove it when the service panel already has the MBJ.

On the other hand, if the Gateway is used as a service panel, such as an installation with an East Coast style separate meter socket only, then the gateway does need the main bonding jumper installed inside it.


On my install the neutral is bonded to ground at the MSP where there is a grounding rod going to earth below the MSP.

And the TEG2 is also neutral bonded to ground with a second grounding rod going to earth below the TEG2.

Sunrun said they always do ESS this way. I don’t think this is an error on the CAD, I think they’re trained to do this.
 
Upvote 0
Sunrun said they always do ESS this way. I don’t think this is an error on the CAD, I think they’re trained to do this.
They are 100% wrong and this should be fixed. Remove the neutral/ground bond in the TEG2. The extra ground rod can stay, attached to ground, not neutral.

Cheers, Wayne
 
Last edited:
Upvote 0
Page 21 of the Tesla installation manual says otherwise and says to only use the MBJ when the GW2 is installed as service equipment.

I was wrong, it's not a wire in the GW2, it is a little metal bridge with 2 bolts holding it down.


If it isn't obvious by my experience with Sunrun; their designers never read the Tesla Powerwall and Gateway installation manual.
 
Upvote 0
They are 100% wrong and this should be fixed. Remove the neutral/ground bond in the TEG2. The extra ground rod can stay, attached to ground, not neutral.

Cheers, Wayne


Do I have to completely de-energize my home to remove that metal bridge? Like is there actually a one time benefit I may get to flip all 6 disconnects to the open position??

But for real, why would two grounding rods and two neutral to ground bonds within 2 feet of each other actually pose a problem?
 