If an electrician installed your wiring, and if an inspector actually inspected it, then they both need to be fired. The LFMC installation in a garage is dubious and could be a Code violation because it is subject to physical damage, but more troubling is what we can't see. If your electrician fished the 6/3 NM-B in the 3/4" conduit, then it violates the 40% fill rule and could overheat. If he stripped the outer jacket off the NM-B and routed the unmarked conductors through the length of the LMFC, that is also a Code violation. Maybe he transitioned to THHN on the other side of the wall in a j-box. Also, where is the firestopping/vapor barrier? More pix please if possible.