I will be submitting my order today for the Model 3 LR. I would love some feedback good or bad for my plans for wiring the garage outlet. Our hot tub is long gone but the double 50 amp breaker tied together is still in the panel as well has 50 feet of aluminum 6 awg gauge wire. I am going to reroute this to the garage and install a Nema 14-50 wall outlet. A licensed electrician will check/test all connections. Twenty feet of the wiring has to be outdoors against an out door wall. I was going to use conduit here and also put some coax internet and antenna cable in the same conduit. The breakers in the panel are 30 years old but were only used for the 20 years we had the hot tub. Should I have the electrician replace these? How does this all sound?
 
I'm not a fan of Aluminum wiring. And don't assume that 6AWG Aluminum is the equivalent in copper. I'd suggest replacing, if possible.
As to the breakers, age isn't that big of a deal, but then again, they aren't that expensive.
But I wouldn't (and the electrician probably won't let you, since there may be code issues) put the low voltage wires in the same conduit as the high-voltage.
 
  • Like
Reactions: brkaus
I'm not a fan of Aluminum wiring. And don't assume that 6AWG Aluminum is the equivalent in copper. I'd suggest replacing, if possible.
As to the breakers, age isn't that big of a deal, but then again, they aren't that expensive.
But I wouldn't (and the electrician probably won't let you, since there may be code issues) put the low voltage wires in the same conduit as the high-voltage.

Yep, second most of this. Assuming it's going to be inspected, your electrician should know what to do.

There's nothing "wrong" with aluminum for larger stuff like this, since you're unlikely to directly mate it with copper (which is where it's problematic in smaller applications), and most terminal connections at that size are Al/Cu ready. That said, 6ga aluminum in conduit could be touch-and-go codewise for the current capacity you need. Since it's so old, you probably can't easily reference the manufacturer's amp ratings, but based on the stuff they make today, even if the insulation was rated for 90°C (it probably isn't), it'd probably be a little undersized. I'll be surprised if your electrician doesn't replace it.

One other thing you might want to consider: if you're all-in on this EV thing and have to replace the wiring anyway, you might want to have him size the wiring/conduit for 100A@240V for future use (but still a 50A breaker for now). The Model 3 LR onboard charger maxes out at 48A today (if you were using a wall connector- less with the UMC it comes with), but your next car might not. The additional expense to bump the conductor size up is pretty minimal compared to what you're going to pay the electrician...

Oh, and I'd replace the breakers if it were me... You're going to be pulling close to its rated capacity constantly, and old breakers have a tendency to "buzz" for various reasons.

For the low voltage stuff: even though there are limited situations where it can be legal to share conduit, don't do it. You'll likely have to use a much more expensive low voltage wire to be code-compliant, and many inspectors just don't like it (even when perfectly code compliant). Plus, you're opening yourself up to all sorts of potential noise issues on the low voltage stuff with a long parallel run in such close proximity to high voltage AC.
 
Last edited:
I have a 120ft run from the panel to the garage. My electrician charged $525 to run 6 guage 4 conductor wire, 50amp breaker, NEMA 15-40 outlet, 3/4" conduit in the exposed portion of garage. I have a 200 amp panel and had 2 unused conduits from it up to the attic. He did the job last week in two hours. I priced out the components to do the job myself; would have cost $300 minimum and probably a day or two of my time.
Great deal as far as I'm concerned.